    Condensate as grey water



    Question 1

    I am busy with the design of a green building. One of the methods identified to utilise the condensate water as grey water for the toilets.

    What methods could I use to calculate the amount of water removed from the air per day?

    Thanks.



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: Condensate as grey water

    Theoretically, by applying Mollier chart and some supposed conditions an quantities of cooled air.
    Practically, you have to many varying inputs (temperature, humidity, air quantity.....).

  3. #3
    TRASH101's Avatar
    TRASH101 is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Mar 2007
    Location
    england
    Posts
    397
    Rep Power
    18

    Re: Condensate as grey water

    Because of the limitations and varied quantities of condensate you would be better off having a compensated conventional system perhaps with a float switch and solenoid. Dont know what water by-laws but grey water storage might have micro biological considerations

  4. #4
    Join Date
    Jan 2008
    Location
    Australia
    Posts
    71
    Rep Power
    17

    Re: Condensate as grey water

    Hello Samian,
    I know this sounds rough but as a very general rule I have used the old (1Hp of cooling produces 1 litre of condensate per hour). Its probabley overkill but it has worked.
    It hasn't failed yet.

    I would wait for a more accurate way of calculating condensate from someone else though.

    dsp

  5. #5
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: Condensate as grey water

    Have a look at page 8 of this Sauermann condensate pump handbook.

    Note that the liquid quantity is in US gph.

    http://www.sauermann.us/pdf/Handbook_2006_new.pdf
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  6. #6
    Join Date
    Aug 2007
    Location
    Sydney
    Age
    51
    Posts
    1,094
    Rep Power
    23

    Re: Condensate as grey water

    Here in Sydney I hear they are using condensate for cooling tower makeup, and for the toilets many buildings are going for the waterless uranals - they stink a bit much for me.

  7. #7
    Join Date
    Apr 2006
    Location
    stafford
    Age
    42
    Posts
    985
    Rep Power
    19

    Re: Condensate as grey water

    0.5-0.8 litters per hour hour per kw of duty,i read the other day,also room humidity will be a major factor
    Paul


    "KEEP IT COOL"

  8. #8
    Join Date
    Jun 2007
    Location
    South Africa
    Posts
    80
    Rep Power
    17

    Re: Condensate as grey water

    Hi Guys - thanks for the thoughts and the rules of thumb.

    I should have elaborated further on the refigerated zones, there are Low (at -20C), Medium temp zones (0C and 10C).

    My preliminary condenstate water calc was base on the amount of ice buildup on the coil (up to the defrost). Any thoughts on this method?

  9. #9
    Join Date
    Feb 2008
    Location
    Napa, CA
    Age
    54
    Posts
    33
    Rep Power
    0

    Re: Condensate as grey water

    Quote Originally Posted by samiam View Post
    Question 1

    I am busy with the design of a green building. One of the methods identified to utilise the condensate water as grey water for the toilets.

    What methods could I use to calculate the amount of water removed from the air per day?

    Thanks.
    I like your thinking. Condensate is one thing, condenser water cycles are another. We have been using a dolphin treated evap condensers water as grey water for toilets. We have a pressure storage tank that fills on need. Taking water from the evap condenser, while reducing the hardness levels. Great for both sides.

  10. #10
    Join Date
    Mar 2008
    Location
    Dallas, Oregon
    Age
    72
    Posts
    51
    Rep Power
    17

    Re: Condensate as grey water

    This is a bit off subject, but your question about collecting water from the air reminded me of a water collection system the military is looking into to "tap the air" for water.

    A large bank of vessels filled with desiccant draws water from the air, and when the desiccant is regenerated the water is condensed and filtered for drinking. It is much cheaper and energy efficient than trying to condense water with just refrigeration.

  11. #11
    Join Date
    Mar 2009
    Location
    U.S.A.
    Posts
    320
    Rep Power
    20

    Re: Condensate as grey water

    Meltwater to the toilets....Has a tickle tendency to it. Believe it has been done at some ice rinks with the snow melt from the re-surfacing.

    Used to run meltwater back to a "cold well" in the evap condenser tank, cooled the air compressors and CA driers with it, return was to the "warm" side.

    I have also seen it used to dehumidfy receiving or ante rooms, docks, etc. using a "waste" halocarbon finned coil and a poly tank connected directly to the drain. Q & D +1C Dew Point air.

  12. #12
    Join Date
    Mar 2009
    Location
    U.S.A.
    Posts
    320
    Rep Power
    20

    Re: Condensate as grey water

    Sorry, off topic.

    A lot of studies and papers on the amount of water generated by HG Defrost to help understand the corresponding HS load. Many rules of thumb concerning face area of coil, initial coil temperature and similar.
    Niagara No Frost has a collection of case studies based on the energy usage & cleanliness of their equipment. Some of that on their website; some more at :
    http://www.irc.wisc.edu/ASHRAE-TC105...ddesiccant.pdf


    Very detailed but based on actual measurements: Wisconsin Doctorate thesis...


    minds.wisconsin.edu/bitstream/handle/1793/7606/hoffenbecker_04.pdf?sequence=1

    The parties in a prolonged study on the effectiveness of hot gas defrost include R. A. Cole; R. Sherif; A. Al-Mutawa.

    Some case studies also with Munters and Harris in terms of process spaces particularly.

  13. #13
    Join Date
    Jan 2006
    Location
    Valrico, Florida
    Posts
    517
    Rep Power
    19

    Re: Condensate as grey water

    On our penthouse units we run the condensate lines back to the evaporative condenser and reuse the water that way,.

  14. #14
    Join Date
    Jun 2006
    Location
    British West Indies
    Posts
    545
    Rep Power
    18

    Re: Condensate as grey water

    outside of slime and biologicals on the cooling coil that is distilled water. There are commercially available systems to turn it into potable water

    Its all about climate. I have some 2250 CFM 100% outside air units, that will produce about 400 US gallons a day in the humid rainy season
    Take the V out of HVAC and you are left with a HAC job

  15. #15
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    63
    Posts
    2,212
    Rep Power
    20

    Re: Condensate as grey water

    There are commercially available systems to turn it into potable water
    Could you please provide some links to such commercial systems? This would be very useful to me. Many thanks.
    Last edited by desA; 17-04-2009 at 05:30 AM.

  16. #16
    Join Date
    Sep 2008
    Location
    Canada
    Posts
    811
    Rep Power
    18

    Re: Condensate as grey water

    Quote Originally Posted by sterl View Post
    Sorry, off topic.

    A lot of studies and papers on the amount of water generated by HG Defrost to help understand the corresponding HS load. Many rules of thumb concerning face area of coil, initial coil temperature and similar.
    Niagara No Frost has a collection of case studies based on the energy usage & cleanliness of their equipment. Some of that on their website; some more at :
    www.irc.wisc.edu/ASHRAE-TC105/programs/Liquiddesiccant.pdf


    Very detailed but based on actual measurements: Wisconsin Doctorate thesis...


    minds.wisconsin.edu/bitstream/handle/1793/7606/hoffenbecker_04.pdf?sequence=1

    The parties in a prolonged study on the effectiveness of hot gas defrost include R. A. Cole; R. Sherif; A. Al-Mutawa.

    Some case studies also with Munters and Harris in terms of process spaces particularly.
    Optimization of hot gas defrosting is complicated issue. This master's thesis just touch the surface.

  17. #17
    Join Date
    Jun 2006
    Location
    British West Indies
    Posts
    545
    Rep Power
    18

    Re: Condensate as grey water

    Quote Originally Posted by desA View Post
    Could you please provide some links to such commercial systems? This would be very useful to me. Many thanks.
    Munters was one vendor, i looked on the site but I am afraid you will have to contact a representative
    Take the V out of HVAC and you are left with a HAC job

  18. #18
    Join Date
    Jun 2006
    Location
    British West Indies
    Posts
    545
    Rep Power
    18

    Re: Condensate as grey water

    Take the V out of HVAC and you are left with a HAC job

Similar Threads

  1. Hoshizaki Ice Maker
    By Abe in forum Legal-Business-Marketing
    Replies: 19
    Last Post: 01-05-2010, 03:27 AM
  2. Fact or Fiction
    By david.findlay in forum Fundamentals
    Replies: 40
    Last Post: 09-03-2009, 07:19 PM
  3. cold river water
    By eftimios in forum Fundamentals
    Replies: 8
    Last Post: 09-11-2008, 07:37 PM
  4. open cycle R718 A/C that also provides high purity water?
    By star882 in forum Technical Speculations
    Replies: 7
    Last Post: 27-07-2006, 04:18 AM
  5. Building a wine cabinet
    By Rory in forum Technical Discussions
    Replies: 38
    Last Post: 13-07-2004, 08:28 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •