12-02-2008, 05:54 PM #1
Condensate as grey water
Question 1
I am busy with the design of a green building. One of the methods identified to utilise the condensate water as grey water for the toilets.
What methods could I use to calculate the amount of water removed from the air per day?
Thanks.
-
12-02-2008, 06:06 PM #2
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: Condensate as grey water
Theoretically, by applying Mollier chart and some supposed conditions an quantities of cooled air.
Practically, you have to many varying inputs (temperature, humidity, air quantity.....).
-
12-02-2008, 06:43 PM #3
Re: Condensate as grey water
Because of the limitations and varied quantities of condensate you would be better off having a compensated conventional system perhaps with a float switch and solenoid. Dont know what water by-laws but grey water storage might have micro biological considerations
-
12-02-2008, 09:36 PM #4
Re: Condensate as grey water
Hello Samian,
I know this sounds rough but as a very general rule I have used the old (1Hp of cooling produces 1 litre of condensate per hour). Its probabley overkill but it has worked.
It hasn't failed yet.
I would wait for a more accurate way of calculating condensate from someone else though.
dsp
-
13-02-2008, 12:13 AM #5
Re: Condensate as grey water
Have a look at page 8 of this Sauermann condensate pump handbook.
Note that the liquid quantity is in US gph.
http://www.sauermann.us/pdf/Handbook_2006_new.pdfBrian - Newton Abbot, Devon, UK
Retired March 2015
-
13-02-2008, 06:56 AM #6
Re: Condensate as grey water
Here in Sydney I hear they are using condensate for cooling tower makeup, and for the toilets many buildings are going for the waterless uranals - they stink a bit much for me.
-
14-02-2008, 08:18 AM #7
Re: Condensate as grey water
0.5-0.8 litters per hour hour per kw of duty,i read the other day,also room humidity will be a major factor
Paul
"KEEP IT COOL"
-
14-02-2008, 10:06 PM #8
Re: Condensate as grey water
Hi Guys - thanks for the thoughts and the rules of thumb.
I should have elaborated further on the refigerated zones, there are Low (at -20C), Medium temp zones (0C and 10C).
My preliminary condenstate water calc was base on the amount of ice buildup on the coil (up to the defrost). Any thoughts on this method?
-
17-02-2008, 08:29 PM #9
Re: Condensate as grey water
I like your thinking. Condensate is one thing, condenser water cycles are another. We have been using a dolphin treated evap condensers water as grey water for toilets. We have a pressure storage tank that fills on need. Taking water from the evap condenser, while reducing the hardness levels. Great for both sides.
-
05-03-2008, 05:16 AM #10
Re: Condensate as grey water
This is a bit off subject, but your question about collecting water from the air reminded me of a water collection system the military is looking into to "tap the air" for water.
A large bank of vessels filled with desiccant draws water from the air, and when the desiccant is regenerated the water is condensed and filtered for drinking. It is much cheaper and energy efficient than trying to condense water with just refrigeration.
-
15-04-2009, 06:47 PM #11
Re: Condensate as grey water
Meltwater to the toilets....Has a tickle tendency to it. Believe it has been done at some ice rinks with the snow melt from the re-surfacing.
Used to run meltwater back to a "cold well" in the evap condenser tank, cooled the air compressors and CA driers with it, return was to the "warm" side.
I have also seen it used to dehumidfy receiving or ante rooms, docks, etc. using a "waste" halocarbon finned coil and a poly tank connected directly to the drain. Q & D +1C Dew Point air.
-
15-04-2009, 08:15 PM #12
Re: Condensate as grey water
Sorry, off topic.
A lot of studies and papers on the amount of water generated by HG Defrost to help understand the corresponding HS load. Many rules of thumb concerning face area of coil, initial coil temperature and similar.
Niagara No Frost has a collection of case studies based on the energy usage & cleanliness of their equipment. Some of that on their website; some more at :
http://www.irc.wisc.edu/ASHRAE-TC105...ddesiccant.pdf
Very detailed but based on actual measurements: Wisconsin Doctorate thesis...
minds.wisconsin.edu/bitstream/handle/1793/7606/hoffenbecker_04.pdf?sequence=1
The parties in a prolonged study on the effectiveness of hot gas defrost include R. A. Cole; R. Sherif; A. Al-Mutawa.
Some case studies also with Munters and Harris in terms of process spaces particularly.
-
16-04-2009, 07:36 PM #13
Re: Condensate as grey water
On our penthouse units we run the condensate lines back to the evaporative condenser and reuse the water that way,.
-
17-04-2009, 05:14 AM #14
Re: Condensate as grey water
outside of slime and biologicals on the cooling coil that is distilled water. There are commercially available systems to turn it into potable water
Its all about climate. I have some 2250 CFM 100% outside air units, that will produce about 400 US gallons a day in the humid rainy seasonTake the V out of HVAC and you are left with a HAC job
-
17-04-2009, 05:26 AM #15
Re: Condensate as grey water
There are commercially available systems to turn it into potable waterLast edited by desA; 17-04-2009 at 05:30 AM.
-
18-04-2009, 12:51 AM #16
-
26-04-2009, 01:15 AM #17
-
26-04-2009, 04:51 AM #18
Re: Condensate as grey water
Take the V out of HVAC and you are left with a HAC job
Similar Threads
-
Hoshizaki Ice Maker
By Abe in forum Legal-Business-MarketingReplies: 19Last Post: 01-05-2010, 03:27 AM -
Fact or Fiction
By david.findlay in forum FundamentalsReplies: 40Last Post: 09-03-2009, 06:19 PM -
cold river water
By eftimios in forum FundamentalsReplies: 8Last Post: 09-11-2008, 06:37 PM -
open cycle R718 A/C that also provides high purity water?
By star882 in forum Technical SpeculationsReplies: 7Last Post: 27-07-2006, 04:18 AM -
Building a wine cabinet
By Rory in forum Technical DiscussionsReplies: 38Last Post: 13-07-2004, 08:28 PM