    I am doing a project to optimize the power consumption of a water cooled chiller . But my consultant told me that i can first make a model to estimate the power consumption of a chiller base on the change of (1) chilled water flow, (2) chilled water supply temper, (3) chilled water return temperature, (4) condenser water temperature(entering chiller), (5) Condenser flow.
    What is the benefits in estimating power consumption of the chiller?
    Once i know the power consumption under some conditions, what i can do to lower the chiller power consumption?
    Thank You
    Sep 2008
    Canada
    765
    12
    Re: Power consumption of Chiller
    Quote Originally Posted by adrian116 View Post
    Dear all
    Thank You
    You have to determine an efficiency of the chiller. Efficiency is power use per unit of refrigeration. Better efficiency will save energy. Probably, a chiller has two major variables. Refrigeration load and ambient conditions. Ref. load influence on water flow and tem. in and out. Ambient con. influence on cond. water flow and cond. water temperature. Choose the best efficiencies(changing flows and temperatures) at certain ref.load and amb. cond.
    adrian116's Avatar
    adrian116 Guest
    Thanks for replying.
    Do you mean to find the highest efficiency with the power estimated by the model by changing the variables? But how this result compare to the real one?
    I am confusing why estimation is needed instead of investigate the real chiller directly?
    adrian116's Avatar
    adrian116 Guest
    Can i say that the estimation is used to simulate the chiller in order to find the highest efficiency? Is it reasonable?
    I have found many paper about power optimization of chiller and conclude following points:
    (1) lower the condenser water temperature. This can be modify by replacing the cooling tower with a lower energy and larger fan. VSD is also preferred.
    (2) Increase the flow of condenser water. But why?
    (3) chiller sequencing. To find the efficiency of chillers in a plant system and setup the most power saving sequencing.
    (4) keep the chilled water supply temperature as high as possible. But why?
    (5) operating chillers in the max-cap range. Is this mean a chiller is more efficient at full load than part load? Why?
    Sep 2008
    Canada
    765
    12
    If you have a good model of the plant, you can calculate power use by changing the value of variables and choose the most efficient values. You need millions tests on real plant to explore all combinations of variables.
    Sep 2008
    Canada
    765
    12
    1. It should be balance. Larger tower require more capitals and more fan power. Sometimes additional fan power exceed compressor energy savings at lower condensing pressure.
    2. Water flow should be balanced as well. Additional flow can lower cond. pressure, but require additional pump energy. Total power(compressors+fans+pumps) should be minimum.
    3. Sequence should be chosen to avoid part-load operation.
    4. The higher water temperature, the higher suction pressure can be and compressor efficiency will improve.
    5. Screw compressors have poor part load performance especially at capacity lower than 50%. Very often pump don't have VFDs and their power use unchanged at different loads. At part load, total plant efficiency will be lower.
    adrian116's Avatar
    adrian116 Guest
    Quote Originally Posted by Segei View Post
    Thank for replying.
    for (4) why higher water temperature will result highter suction pressure?
    for (5) Why part-load is inefficienct compare with full load for a single chiller?
    Besides those five points. Do you have any suggestion in improving a chiller plant system to have significant savings?
    Thank you
    Sep 2008
    Canada
    765
    12
    Thank for replying.
    Thank you
    Assume that water flow is constant. Compressor is designed for certain ref. load or certain temp. difference. For example. Design temp. difference is 5degC. If water 2degC, suction temp. will be 7degC. If water is 5degC, suction temp. will be 10degC.
    About part-load.
    Full load. Compressor 100TR(ton refrigeration) and 200HP(horse power). Water pump 10HP, condenser fan 20HP. Total power use 230HP. Efficiency 230/100=2.3HP/TR
    50% load. Compressor 50TR, 120HP. Pump 10HP, fan 10HP. Total power 140HP. Efficiency 140/50=2.8HP/TR
    Full load is more efficient than 50% load.
  1. York Chiller startup when on Emergency Power
    By Apollo10 in forum Trouble Shooting
    Last Post: 22-12-2008, 08:13 PM
  2. Replies: 0
    Last Post: 17-11-2008, 09:10 PM
  3. SR2 50 models electric SBY diagonostics made simple
    By absolute-zero in forum Transport
    Last Post: 04-01-2008, 06:11 PM
  4. Daikin KRP2A61 Card Power consumption
    By EddieC in forum Air Conditioning
    Last Post: 19-08-2006, 04:08 PM