    Supermarket heat load calculation



    How to calculate air change heat loss thru doors of supermarket.
    It has two doors which are frequently open by motion detector of these dimensions: 3mx2,2m

    My taught is to calculate only required air changes by space and make supply ventilation flow slightly higher than discharge air flow to make space in slight overpressure and heat loss thru the doors would then be only difference in air flow between supply and discharge air. And maybe to install air curtains at doors to decrease losses.
    Also, Heat recovery coil would be mounted in supply/discharge ventilation.

    Am I right, or I have something wrong?



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Supermarket heat load calculation

    Nope, I think that you have covered it.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Supermarket heat load calculation

    Quote Originally Posted by Brian_UK View Post
    Nope, I think that you have covered it.

    Thanks Brian!

  4. #4
    Join Date
    Mar 2008
    Location
    England
    Age
    68
    Posts
    250
    Rep Power
    17

    Re: Supermarket heat load calculation

    Hi Nike. Do I take it you have some exhaust air as well as return, supply and fresh air? If so what are the percentages? Also is their any free cooling - I assume we are talking about A/C here and not a cold room.
    Normal procedure is to slighly over pressurize the conditioned area to avoid untreated outside air coming in through opening doors etc. Fresh air comes into system via the AHU (perhaps with pre-heat in winter), mixed with % of return air and treated via main cooling / heating coils.
    A door curtain would be a good idea to prevent wind assisted ingress and to minimise conditioned air loss. Electric heater may be needed for winter operation. Alternatively Mitsubishi now offer a Heat Pump heating only Air curtain system. Quite expensive compared to an electic heater curtain but will save a lot of money in running costs. Details are on the UK Mitsi web site under Products, Mr.Slim, Air curtain - its a downloadable PDF. Daikin also do one now but their's can only be connected to a VRV system. Mitsi's is a 1:1 split system.
    If in doubt read the instructions. If still in doubt follow them.

  5. #5
    chinatim's Avatar
    chinatim Guest

    Re: Supermarket heat load calculation

    Quote Originally Posted by nike123 View Post
    How to calculate air change heat loss thru doors of supermarket.
    It has two doors which are frequently open by motion detector of these dimensions: 3mx2,2m

    My taught is to calculate only required air changes by space and make supply ventilation flow slightly higher than discharge air flow to make space in slight overpressure and heat loss thru the doors would then be only difference in air flow between supply and discharge air. And maybe to install air curtains at doors to decrease losses.
    Also, Heat recovery coil would be mounted in supply/discharge ventilation.

    Am I right, or I have something wrong?
    me doing the similiar as you, however i also test if the ventilator flow then decided the plan.

  6. #6
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Supermarket heat load calculation

    Quote Originally Posted by Greengrocer View Post
    Hi Nike. Do I take it you have some exhaust air as well as return, supply and fresh air? If so what are the percentages? Also is their any free cooling - I assume we are talking about A/C here and not a cold room.
    Normal procedure is to slighly over pressurize the conditioned area to avoid untreated outside air coming in through opening doors etc. Fresh air comes into system via the AHU (perhaps with pre-heat in winter), mixed with % of return air and treated via main cooling / heating coils.
    A door curtain would be a good idea to prevent wind assisted ingress and to minimise conditioned air loss. Electric heater may be needed for winter operation. Alternatively Mitsubishi now offer a Heat Pump heating only Air curtain system. Quite expensive compared to an electic heater curtain but will save a lot of money in running costs. Details are on the UK Mitsi web site under Products, Mr.Slim, Air curtain - its a downloadable PDF. Daikin also do one now but their's can only be connected to a VRV system. Mitsi's is a 1:1 split system.

    The space is medium size (360m^2). It is for space cooling. Percentages I don't know since that is not my project, it is principle discussion with my colleague on local newsgroup.
    It will have fresh air supply and exhaust air on heat recovery coil, and I suppose, fresh supply air after passed recuperation will be additionally conditioned with split system air conditioner duct fan coil.
    Space will be heated/cooled with split-system air conditioners which only works on indoor air recirculation.
    Door air curtain will probably have electric heaters for heating season
    VRV systems are to expensive here for our average businessmen, since our society is in "primitive accumulation of capital" phase after change of our economic system !
    Last edited by nike123; 23-04-2009 at 09:32 AM.

  7. #7
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Supermarket heat load calculation

    Quote Originally Posted by chinatim View Post
    me doing the similiar as you, however i also test if the ventilator flow then decided the plan.
    I am afraid that I don't understand your point.

Similar Threads

  1. Replies: 3
    Last Post: 31-03-2009, 06:56 PM
  2. Heat transfer coefficient - Coolpack
    By Graham in forum Fundamentals
    Replies: 10
    Last Post: 28-05-2008, 01:08 AM
  3. Heat Load calculation for residential jobs
    By Herschmidt in forum Air Conditioning
    Replies: 2
    Last Post: 12-05-2008, 11:50 PM
  4. frostles heat pump
    By Lc_shi in forum New Technologies
    Replies: 27
    Last Post: 31-03-2008, 07:53 AM
  5. oil in tank heat load calculation
    By abbasi in forum Fundamentals
    Replies: 7
    Last Post: 13-06-2005, 08:36 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •