    2 stage compressor & pump downs



    Hello,
    i am working with a walk-in freeze with 3 LH124/S4G12.2-35P condensing units.
    When these units pumpdown sometimes the receiver (bottom) sight glass becomes

    empty.
    When running, both sightglasses are ok. Receiver and liquid line glass.
    what would cause this to happen?

    Unit was installed with 2 low pressure switches.

    1 Danfoss KP1; sensor goes to the oil fill hole, according to Bitzer

    diagrams. so it senses the interstage/ crankcase pressure.
    cut-in = 20 psig
    differential = 15 psig

    1 Danfoss KP15 (hi & lo pressure switch)
    Low pressure sensor attached to low side (on the suction head), i assume

    sensing suction pressure.
    cut-in = 2-3 psig
    differential = 18 psig

    can someone why there is 2 lo pressure switches?
    and what should the correct temperature/ pressure setting be?
    why does the receiver empty sometimes on pumpdown?

    gas= R22
    set temp -23 C/ -10 F

    thanks for any help,
    bnhz



  2. #2
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: 2 stage compressor & pump downs

    Sometimes one LP switch is used for pump down stop and another LP switch of low pressure trip. The latter is usually having a lower setting than the former.

    I'm honest when I say that a LP switch at the interstage is new to me , but it can well be the pump down LP switch, or the setpoint LP switch for a blast freezer regulated on crankcase pressure.

  3. #3
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: 2 stage compressor & pump downs

    Quote Originally Posted by bnhz View Post
    Hello,
    i am working with a walk-in freeze with 3 LH124/S4G12.2-35P condensing units.
    When these units pumpdown sometimes the receiver (bottom) sight glass becomes

    empty.
    When running, both sightglasses are ok. Receiver and liquid line glass.
    what would cause this to happen?

    Unit was installed with 2 low pressure switches.

    1 Danfoss KP1; sensor goes to the oil fill hole, according to Bitzer

    diagrams. so it senses the interstage/ crankcase pressure.
    cut-in = 20 psig
    differential = 15 psig

    1 Danfoss KP15 (hi & lo pressure switch)
    Low pressure sensor attached to low side (on the suction head), i assume

    sensing suction pressure.
    cut-in = 2-3 psig
    differential = 18 psig

    can someone why there is 2 lo pressure switches?
    and what should the correct temperature/ pressure setting be?
    why does the receiver empty sometimes on pumpdown?

    gas= R22
    set temp -23 C/ -10 F

    thanks for any help,
    bnhz
    Hi,
    Could you tell me where the liquid line solenoid valve is located, in relation to the other components in the liquid line?
    Cheers Grizzly

  4. #4
    bnhz's Avatar
    bnhz Guest

    Re: 2 stage compressor & pump downs

    the liquid line solenoid is located within 5 ft (of liquid line) of the condensing unit, after the drier.

  5. #5
    Join Date
    Nov 2005
    Location
    belgium
    Posts
    61
    Rep Power
    0

    Re: 2 stage compressor & pump downs

    a pressostat at the interstage, i never see this before. two pressostats, indeed, one for the pumpdown and one for safety. is the condensor outside, the receiver inside, and there is no return valva: when the condensor gets to cold cause the fans ar working, maybe no hp pressostats or something, the condensorpressure is lower than the receiverpressure, the ***** goes back from the receiver to the condensor

  6. #6
    Join Date
    Mar 2009
    Location
    U.S.A.
    Posts
    320
    Rep Power
    20

    Re: 2 stage compressor & pump downs

    Is there an unload solenoid or even a bypass solenoid for the low stage cylinders?

    I'm thinking the interstage pressure switch prevents the low stage cylinders from pumping to the high stage until the IS pressure has DROPPED to set point; so the thing doesn't overload its motor during re-start and pulldown.

    Don't know about the Bitzers but other machines run that way.

  7. #7
    bnhz's Avatar
    bnhz Guest

    Re: 2 stage compressor & pump downs

    I am also waiting to hear from Bitzer about this situation. The only other thing that might help about the double low pressure switches is saying that these units are in Iraq and we have found some terrible mistakes on many pieces of equipment shipped here from nearby countries or installed by a locals.
    this whole setup may be just another bad install. it would not surprise me.
    things are just not done like they are the USA here.

  8. #8
    bnhz's Avatar
    bnhz Guest

    Re: 2 stage compressor & pump downs

    nando,
    the receiver is outside with the condenser.
    the only other solenoid in this system besides the pumpdown slnd is the subcooler and compressor cooling solenoid

  9. #9
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: 2 stage compressor & pump downs

    Hi bnhz,

    This 2 stage BITZER compressors only accept a maximum corresponding suction pressure of -20ºC (for R22) and -25ºC (for R404A/R507).

    Maybe the person who have installed the equipment thought that the crankcase is at the same LP pressure and try to protect against high suction pressure with a KP1 that would switch off the compressor by electrical commands.

    Or maybe the person wants to protect against high intermediate pressure. But I think this makes sense if the cranckase is at the LP pressure and so the high pressure piston and other parts of them suffer high mechanical stress.

    " Danfoss KP1; sensor goes to the oil fill hole, according to Bitzer diagrams" Can you show me the diagram? I think I've never see that.

    About sometimes the receiver liquid is empty, since the condenser and receiver are ate same ambient temperature, an explanation could be the liquid goes almost all to the evaporators...and maybe the compressors are not be hammered with liquid because there is a good suction liquid separator...just an idea...however is strange because you would note the lack of liquid in the receiver in the first 5...10...15 minutes.

Similar Threads

  1. Building a 3 stage cascade
    By NoL in forum CPU Overclockers
    Replies: 9
    Last Post: 27-03-2009, 08:42 PM
  2. Replies: 14
    Last Post: 27-08-2008, 08:57 PM
  3. frostles heat pump
    By Lc_shi in forum New Technologies
    Replies: 27
    Last Post: 31-03-2008, 07:53 AM
  4. Single stage Vs 2 stage comp rack
    By Kevin Yeo in forum Supermarket Refrigeration
    Replies: 0
    Last Post: 01-02-2007, 03:05 PM
  5. Two Stage Thermostat for Heat pump
    By Franzfernando in forum Electrical
    Replies: 3
    Last Post: 02-11-2006, 12:20 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •