21-04-2009, 09:45 AM #1
help me please
Hi .I have centrifugal liquid chiller when i complete recharging and restart work for 2 hours then shutdown and display (high oil flow) then try restart and shutdown againe and (high oil flow).what is the problem?
-
21-04-2009, 07:51 PM #2
Re: help me please
Is it not high oil flow temperature. Check the oil cooler.
-
22-04-2009, 10:42 PM #3
Re: help me please
Thank u
please can you explaine the realation between high oil flow and oil cooler and what is the problem in the oil cooler that maybe cause this .
-
23-04-2009, 04:20 PM #4
Re: help me please
Hi
It cann't be HIGH OIL FLOW !!!
These safety shutdowns require the
operator to manually reset the Control Centre prior to
1. Oil - High Temperature
2. Low Temperature
3. Low Differntial Pressure
4 High Differntial Pressure
5. Pump Pressure Transducer out of Range
6. Sump Pressure Transducer Out of Range
7. Differntial Pressure Calibration
8. Variable Speed Pump-Pressure Setpoint Not Achieved
If the chiller shuts down on aCYCLING shutdown, the
chiller will automatically restart when the cycling
condition is removed. These shutdowns do not require
the operator to manually reset the control centre prior to
restarting the chiller.
1 Oil – Low Temperature Differential or Low Temperature
-
24-04-2009, 12:03 AM #5
Re: help me please
thank
can u explaine manually reset the Control Centre method please.
Note model (YK EB EB H5 5CP D)
-
24-04-2009, 09:55 AM #6
Re: help me please
The purpose of the oil cooler is to remove heat from the oil that has been picked up from the bearings. If the oil cooler is not working the oil temperature will gradually increase and viscocity will decrease, at a predetermined temperature the chiller control will reach its trip point for oil supply temperature. This maybe at 60c,however I am not familiar with this particular machine. The oil cooler can be found on the oil supply pipework somewhere and maybe water cooled. Check oil cooler solenoid,control valve and any strainer. However, with the limited info you have supplied it is only possible to guess.
-
24-04-2009, 12:09 PM #7
-
26-04-2009, 10:11 PM #8
Re: help me please
HI YORK-Engineer
You said These safety shutdowns require the
operator to manually reset the Control Centre prior to restarting the chiller.
Do you know how to do that?