    help me please



    Hi .I have centrifugal liquid chiller when i complete recharging and restart work for 2 hours then shutdown and display (high oil flow) then try restart and shutdown againe and (high oil flow).what is the problem?



  2. #2
    Join Date
    Jul 2008
    Location
    UK
    Age
    60
    Posts
    94
    Rep Power
    16

    Re: help me please

    Is it not high oil flow temperature. Check the oil cooler.

  3. #3
    Join Date
    Apr 2009
    Location
    iraq
    Age
    41
    Posts
    11
    Rep Power
    0

    Re: help me please

    Thank u
    please can you explaine the realation between high oil flow and oil cooler and what is the problem in the oil cooler that maybe cause this .

  4. #4
    York-Engineer's Avatar
    York-Engineer Guest

    Re: help me please

    Hi
    It cann't be HIGH OIL FLOW !!!

    These safety shutdowns require the
    operator to manually reset the Control Centre prior to
    restarting the chiller.

    1. Oil - High Temperature
    2. Low Temperature
    3. Low Differntial Pressure
    4 High Differntial Pressure
    5. Pump Pressure Transducer out of Range
    6. Sump Pressure Transducer Out of Range
    7. Differntial Pressure Calibration
    8. Variable Speed Pump-Pressure Setpoint Not Achieved


    If the chiller shuts down on a
    CYCLING shutdown, the
    chiller will automatically restart when the cycling
    condition is removed. These shutdowns do not require
    the operator to manually reset the control centre prior to

    restarting the chiller.

    1 Oil – Low Temperature Differential or Low Temperature


  5. #5
    Join Date
    Apr 2009
    Location
    iraq
    Age
    41
    Posts
    11
    Rep Power
    0

    Re: help me please

    thank
    can u explaine manually reset the Control Centre method please.
    Note model (YK EB EB H5 5CP D)

  6. #6
    Join Date
    Jul 2008
    Location
    UK
    Age
    60
    Posts
    94
    Rep Power
    16

    Re: help me please

    Quote Originally Posted by engalmohannad View Post
    Thank u
    please can you explaine the realation between high oil flow and oil cooler and what is the problem in the oil cooler that maybe cause this .
    The purpose of the oil cooler is to remove heat from the oil that has been picked up from the bearings. If the oil cooler is not working the oil temperature will gradually increase and viscocity will decrease, at a predetermined temperature the chiller control will reach its trip point for oil supply temperature. This maybe at 60c,however I am not familiar with this particular machine. The oil cooler can be found on the oil supply pipework somewhere and maybe water cooled. Check oil cooler solenoid,control valve and any strainer. However, with the limited info you have supplied it is only possible to guess.

  7. #7
    Join Date
    Apr 2009
    Location
    iraq
    Age
    41
    Posts
    11
    Rep Power
    0

    Re: help me please

    Quote Originally Posted by ptsac View Post
    The purpose of the oil cooler is to remove heat from the oil that has been picked up from the bearings. If the oil cooler is not working the oil temperature will gradually increase and viscocity will decrease, at a predetermined temperature the chiller control will reach its trip point for oil supply temperature. This maybe at 60c,however I am not familiar with this particular machine. The oil cooler can be found on the oil supply pipework somewhere and maybe water cooled. Check oil cooler solenoid,control valve and any strainer. However, with the limited info you have supplied it is only possible to guess.
    I have a good experience in the lubrication system for chiller. I check the cooler if there is a problem in the cooling oil to have a high oil temperature is not high oil flow.
    Thank you
    "

  8. #8
    Join Date
    Apr 2009
    Location
    iraq
    Age
    41
    Posts
    11
    Rep Power
    0

    Re: help me please

    HI YORK-Engineer
    You said These safety shutdowns require the
    operator to manually reset the Control Centre prior to restarting the chiller.
    Do you know how to do that?