Does anybody know what amp circuit breaker need's to be fitted for this unit? daiken FTXS90J wall hung split inverter
Thanks
-
23-01-2011, 10:15 AM #2
Re: daiken FTXS90J wall hung split inverter
As the unit draws 4340watts (18amos) i would use a 25amp c/breaker with 4mm cable.
LawrieRemember we are here for a good time, not a long time.
Trust me i'm a Fridgy.
-
23-01-2011, 03:46 PM #3
Re: daiken FTXS90J wall hung split inverter
id go 20a d type-motor rated even though its inverter driven. the length of cable run will have an effect on the size of cable.