    daiken FTXS90J wall hung split inverter



    Does anybody know what amp circuit breaker need's to be fitted for this unit? daiken FTXS90J wall hung split inverter
    Thanks



  2. #2
    Join Date
    Feb 2009
    Location
    Australia
    Posts
    273
    Rep Power
    16

    Re: daiken FTXS90J wall hung split inverter

    As the unit draws 4340watts (18amos) i would use a 25amp c/breaker with 4mm cable.
    Lawrie
    Remember we are here for a good time, not a long time.
    Trust me i'm a Fridgy.

  3. #3
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,707
    Rep Power
    45

    Re: daiken FTXS90J wall hung split inverter

    id go 20a d type-motor rated even though its inverter driven. the length of cable run will have an effect on the size of cable.