    Post Condenser not Heating



    I am new in the refrigeration trade, barely 1 week. I need some help on the possible causes of the problem I encountered in the freezer I was working on. 1) Evaporator is not cooling. There was no heat coming coming out of the condenser. However, Compressor is running. 2) How to isolate/make a jumper on a LP/HP pressure switch in order to know if the problem is the pressure switch and not the compressor? Many thanks.



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Condenser not Heating

    Pressure switches do not do any work it is only the compressor that moves the refrigerant around.

    Do you have any access ports on the pipework to enable system pressures/temperatures to be measured?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Mar 2008
    Location
    United Kingdom
    Posts
    51
    Rep Power
    17

    Re: Condenser not Heating

    Sounds pretty obvious from your description that either there is no gas in the system or the compressor is not pumping. Fit high and low side gauges to obtain pressure readings and post your findings back here, I'm sure you will find your answer. If the system has no gas in it then firstly it should not be running and secondly you have a leak(s) which you must locate and repair.

  4. #4
    Join Date
    Jan 2006
    Location
    Valrico, Florida
    Posts
    509
    Rep Power
    19

    Re: Condenser not Heating

    I dont know how to put this without sounding like an arshole; but have you any kind of training at all?

  5. #5
    Join Date
    Apr 2007
    Location
    england
    Age
    36
    Posts
    371
    Rep Power
    23

    Re: Condenser not Heating

    Firstly... If the Evaporator is not getting cold and the condenser is not getting warm, no refrigeration is taking place. Very common and may well be a poor pumping compressor or SOG....(short of gas).

    The Lp/Hp Switch this does not directly affect the movement of refrigerant, the live feed for the compressor or compressor contactor will be wired through the LP/HP switch, if tripped H/P or L/P compressor will not run.

    If the compresor is running then your deffinately not tripped H/P, there may not be a L/P switch fitted just double check....

    This would indicate a buggered compressor...not pumping!

    Without being there we cant provide diagnosis, stick some gauges on the system and see what she doing, check for positive pressure and your temperatures including L/P H/P set points on the pressure switch.


    IF YOUR ONLY IN THE GAME 1 WEEK THE ENGINEER TEACHING YOU SHOULD BE DOING THIS IT ALL TAKES TIME TO LEARN

  6. #6
    Join Date
    May 2001
    Location
    glenrothes, scotland
    Age
    63
    Posts
    11
    Rep Power
    0

    Re: Condenser not Heating

    i think you should leave well alone before you hurt yourself, thats pretty basic refrigeration.
    AJ

  7. #7
    Join Date
    Nov 2007
    Location
    Saudi arabia
    Posts
    20
    Rep Power
    0

    Re: Condenser not Heating

    charge some refrigerant n notice air out
    temp-see site glass if there is notice if bubbling try simple pressure test mentioned by a guy here

  8. #8
    Join Date
    Apr 2007
    Location
    england
    Age
    36
    Posts
    371
    Rep Power
    23

    Re: Condenser not Heating

    You need to accertain wether you have a knackered compressor:

    Gauges showing positive pressure? -------Test operation of compressor, if no movement in pressure compressor (possibly) not pumping.

    Compressor runs------ pressures on gauges drops into a vaccum and no cooling on EVP or heat on COND (possibly) system blockage or SOG (short on gas) , check filter drier, expansion device (TEV, Capillary)

    Gauges showing NO pressure?------- Carry out a good OFN (oxygen free nitrogen) pressure test, look for pressure drop, check all suspect joints, poorly brazed joints, oil stained areas. With Leak detection spray or prefered method of leak testing.

    If leak is found and component is replaceable or the leak is repairable, then do so.

    Carry out another pressure test using OFN, and leave for a good period of time and look for pressure drop. If all seems ok, pull a vaccum on the system and recharge to rating plate.

    Run the unit and look for cooling on the EVP and heat at the COND, compressor may have failed if the unit has lost all its charge and no L/P protection has been fitted.
    I would also add some leak detection dye, if the leak was not found.

    This is the sort of thought process you should be going through, there are several shortcuts that me and other A/C & R Guys will do to shorten the job and get a diagnosis quicker.

    Quote Originally Posted by M.Amer View Post
    charge some refrigerant n notice air out
    temp-see site glass if there is notice if bubbling try simple pressure test mentioned by a guy here
    No......
    If the condenser or any pipes have a split or fracture you will merely be venting refrigerant to the atmosphere, this is why a good pressure test with OFN happens first. Just charging the system makes a joke of all the safe handling certificates and paperwork we have to fill out.

    good luck

Similar Threads

  1. Superheat and Subcooling
    By Chunk in forum Fundamentals
    Replies: 42
    Last Post: 15-01-2011, 01:24 AM
  2. Modifying aricond. for heating, cooling and hot water
    By kimusabi in forum Technical Discussions
    Replies: 3
    Last Post: 10-10-2008, 07:28 AM
  3. Air Cooled Condenser Leakage Problem with R-404A
    By RADHAKRISHNARAO in forum Technical Discussions
    Replies: 19
    Last Post: 30-07-2008, 12:21 PM
  4. Plate Heat Exchagers - Condenser
    By Billy Ray in forum Technical Discussions
    Replies: 9
    Last Post: 11-05-2008, 06:16 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •