Results 1 to 8 of 8
    Mar 2004
    fluorecent tubes in fridge/freezers
    hi all,
    can anyone tell me if there is a special type of fluro tube required for a fridges and freezers? do regulars ones ignite okay under these temps? if not, what is the type of tube i need?
    Sep 2003
    ISRAEL
    72
    4,248
    Re: fluorecent tubes in fridge/freezers
    hi slothslag,
    in cold stores down to 0C there should not be any problems with fluorescent lamps ie all components are ok.
    in freezers if you insist of using fluorescent light, you need special electronic starters.
    why not use regular 240 bulbs in a water sealed housing ano starting problems.
    chemi
    Sep 2003
    ISRAEL
    72
    4,248
    here is a link to danfoss electronic ballasts
    chemi
    http://www.danfoss.com/journal/2_00/Bagside.htm
    Aug 2005
    manchester
    47
    Yes electronic starters. Green starters. But make sure the defusser is sealed correctly.
    :eek:
    Oct 2003
    5,630
    34
    Even with electronic starters, ignition is not the problem but it takes quit some time before the lamp reaches it's full lighting capacity (5 minutes at least)
    So if you switch off the lights each time you leave the freezer, then you should better install regular lamps like Chemi said.
    We allways install regular lamps, unless they are kept on the whole day.
    Aug 2005
    northampton
    64
    9
    slothslag
    you need 100 watt rough service lamps these last longer in the sealed units far better than fluorescent lights
    maddfridge
    Nov 2005
    152
    Quote Originally Posted by Jus Walker
    Just make sure it is not sealed air tight
    other wise you will find that it will produce ice inside the diffuser, when the temp rises this will melt causing
    spoilage inside the case.
    A bit of thumb gum in the bores at either end of the tube
    should be fine
    cut your diffuser , fit , but do not seal around it.
    you will need an electronic ballast
    this should do away with the starter.
    we fit standard tubes to our cases , yes it takes 5 minutes for them to reach full illumination, but they are brilliant, these are fitted to freezers that have a set point of -25 degrees celcius.
    Hope this helps !
    The primary function of the design engineer is to make things difficult for the fabricator and impossible for the serviceman.
    Sep 2005
    Singapore
    59
    145
    Here we use GE CWHO (High Output) 6 footed tube, bright & lasting for walk-in chillers.
  1. capillary tubes
    By JimmyMurphy in forum Fundamentals
    Last Post: 24-06-2006, 07:49 AM
  2. Heat transfer through tubes
    By Peter_1 in forum Fundamentals
    Last Post: 27-03-2005, 09:39 PM
  3. Obstructed Capillary Tubes
    By terrygoodrich in forum Trouble Shooting
    Last Post: 17-03-2005, 02:48 PM
  4. reduce thickness of bended copper tubes
    By rlim in forum Air Conditioning
    Last Post: 08-07-2003, 10:58 PM
  5. Replies: 15
    Last Post: 24-10-2002, 06:52 PM