    replacing of r12 with r22 in dwm 1.5 hp



    dear membs
    I have one refrigerator system for ice cream, on the plate of the compressor there is not written type of refregirant,I disassembeled cover and found out on the its expantion valve written R12:
    1)Can I sure refregirant is R12?
    2)If yes ,for getting low tempreture can i replace refregirant with R22 without changing of expantion valve?
    Thanks lot .



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: replacing of r12 with r22 in dwm 1.5 hp

    Quote Originally Posted by a.jalilkhani View Post
    dear membs
    I have one refrigerator system for ice cream, on the plate of the compressor there is not written type of refregirant,I disassembeled cover and found out on the its expantion valve written R12:
    1)Can I sure refregirant is R12?
    Yes

    2)If yes ,for getting low tempreture can i replace refregirant with R22 without changing of expantion valve?
    Thanks lot .
    http://yarchive.net/ac/r22.html

  3. #3
    Join Date
    Oct 2007
    Location
    NZ
    Posts
    85
    Rep Power
    17

    Re: replacing of r12 with r22 in dwm 1.5 hp

    Quote Originally Posted by a.jalilkhani View Post
    dear membs
    I have one refrigerator system for ice cream, on the plate of the compressor there is not written type of refregirant,I disassembeled cover and found out on the its expantion valve written R12:
    1)Can I sure refregirant is R12?
    2)If yes ,for getting low tempreture can i replace refregirant with R22 without changing of expantion valve?
    Thanks lot .
    You really do need to change that TX valve if you put R22 , I think youll find it will either flood back continuously or starve the evap with the wrong TX valve , as for the compressor where do you start those compressors can stall if r12 is replaced with a higher preasure refrigerant and if it does run the head preasure may be 2 high .
    is there any reason why you are not trying I49 instead of r 12 , its ozone friendly and no oil change is needed

  4. #4
    Join Date
    Feb 2008
    Location
    adelaide sth.oz
    Posts
    1,015
    Rep Power
    19

    Re: replacing of r12 with r22 in dwm 1.5 hp

    look out for refrigerant & oil burn.valve plate probably not suitable for refrigerant 22 application.i wouldnt waste my time,use a drop in or retrofit to 134a

Similar Threads

  1. Replacing glass in door on True refrigerator
    By BlueVanACD2005 in forum Commercial
    Replies: 0
    Last Post: 19-01-2009, 07:31 PM
  2. Replacing a pari of compressors ona Carrier 30HR 121
    By Sanshinman in forum Commercial
    Replies: 3
    Last Post: 06-11-2008, 06:50 PM
  3. Do we have some expert in replacing compressors
    By Zahid in forum Air Conditioning
    Replies: 2
    Last Post: 01-07-2008, 07:59 AM
  4. Replacing condensor
    By Rayin in forum New to RE
    Replies: 5
    Last Post: 05-11-2006, 01:49 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •