Thread: cooling water piping system
18-04-2009, 11:12 AM #1
Hi guys,
I'm carrying out a pressure test for 600 ton cooling water steel piping system.
I need to know the effect of temperature drop on the system pressure during the test.
On the copper piping system the relation is 0.1 bar for each 1 degree C, what about the water piping systems.
18-04-2009, 10:45 PM #2
Re: cooling water piping system
Are you conducting an "dry pressure" test or a "wet pressure" test of the water piping system?
19-04-2009, 07:34 AM #3
Effect of temperature on pressure testing will depend on the quality of water used as I had an experience while pressure testing of cooling water pipe 10 Kg/cm2 and would increase to 14 Kg/cm2 and the authorities started questioning why you have increased the pressure.
When we told the pressure has increased on its own, we were asked to investigate and on getting the water analysis it was observed the water used had lot of dissoled gases which was the cause for increasing pressure.
19-04-2009, 12:08 PM #4
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Cooling down the water in a 1000 liter container
By Joep Hogenhout in forum Technical DiscussionsReplies: 29Last Post: 21-04-2009, 01:27 AM -
cooling water TDS
By afeef in forum Technical SpeculationsReplies: 1Last Post: 19-04-2009, 07:38 AM -
Cooling and dehumidifing by chill water
By DEVITG in forum FundamentalsReplies: 8Last Post: 26-09-2008, 02:58 PM -
water cooling storage system
By Lc_shi in forum New TechnologiesReplies: 8Last Post: 28-05-2008, 11:02 PM -