    Install Danfoss TEV



    hi guys just a quickie, i have a danfoss TEV to install in a couple of weeks and the connections are bi-metal, stainless steel outer and copper internal, my question is should i use 40% silver solder/flux to make my conection or should i "braze" it with standard 2% silver (at least 2% is our standard?

    i checked on there web site but it just says solder connection not too sure what they mean by this. any help is much appreciated, thank you.

    ow also while im on the subject, is it normal to lag the external equalization line if the TEV requires it, as this will be as low 1 - 5*c on this install? (R410A Comfort Cooling Air con)

    cheers guys.
    Last edited by SkyWalker; 17-04-2009 at 05:46 PM.



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Install Danfoss TEV

    I would go with 40% because of lower thermal stress at valve (lower melting point).

  3. #3
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Install Danfoss TEV

    both will do.

    The 40% silver is easier and faster . but if you use the 2 % Silfus and add flux powder, no problems just keep the TEV wrapped with a wet piece of cloth.

  4. #4
    Join Date
    Nov 2006
    Location
    At home
    Posts
    181
    Rep Power
    18

    Re: Install Danfoss TEV

    cheers guys much appreciated, what about lagging the equalizing line, is this normally done

  5. #5
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Install Danfoss TEV

    Quote Originally Posted by SkyWalker View Post
    cheers guys much appreciated, what about lagging the equalizing line, is this normally done
    I would say no, it is usually not done.

  6. #6
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: Install Danfoss TEV

    Just installed one of these today and had a nightmare trying to braize it with the 2% silver whilst trying to keep the valve cooled.
    Why do manufacturers not make the stubbs just a little bit longer to make it easier to install them

    I'd go for the 40% silver much easier but at £3 a stick very expensive.
    The difference between genius and stupidity is that genius has its limits.

    Marc

  7. #7
    Join Date
    May 2009
    Location
    UK
    Age
    57
    Posts
    7
    Rep Power
    0

    Re: Install Danfoss TEV

    Don't use your 2% braze alloy (2%Silver/Copper/Phosphorus on the stainless steel - it is not designed for this and you will get failed joints as the Phosphorous forms a brittle intermetallic with the iron in the SS.
    If standard 40%Silver is all you have then I guess use this, but it would be preferable to use an alloy with some Nickel in it such as IPM50N as this reduces the chance of interfacial/crevice corrosion.
    If you need further help - contact me miles.brennan@blueyonder.co.uk

Similar Threads

  1. Too dependent on Danfoss Valves
    By kelvin_27_84 in forum Industrial
    Replies: 8
    Last Post: 24-01-2009, 08:33 PM
  2. York ycaj Danfoss EKS65 phtq info
    By tomireland in forum Trouble Shooting
    Replies: 13
    Last Post: 22-12-2008, 06:47 PM
  3. Problems Danfoss Safetyvalve
    By Bart Nabbe in forum NH3
    Replies: 7
    Last Post: 26-06-2008, 09:05 PM
  4. Daikin VRVIII Install - Sub Contract
    By gwilliamson in forum Air Conditioning
    Replies: 7
    Last Post: 07-02-2008, 09:00 PM
  5. DANFOSS / DEAN and WOOD
    By Grizzly in forum Legal-Business-Marketing
    Replies: 1
    Last Post: 08-12-2007, 07:29 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •