    Hi All,
    Got a problem with a misubishi/daiya Unit
    Model FDCP508HES3 R407 3 phase.

    Problems: Outdoor unit not cutting in, fitted gauges only 20 psi each side poss low on gas, do they have LP Switches ?

    To test my theroy i put in 150psi of OFN & disconnected the wires from the compressor and switched on to see if the contactor pulled in (It Didn't).
    Quick look at the diagram it looks like the A1 of the contactor comes off a relay which switches fom the crank heater to the A1 does this mean the A1 which comes off output 52c on the board only comes on once the crank heater has warmed the pot up. If so how does it tell when its wam enough.
    I couldn't find a leak to left the unit under pressure overnight to see how much it drops.

    There are wo LED's on the board, one red & one green. Nothing going on the the red but the green one just keeps flashing, as far as i am aware this means the system should be OK.

    Just had another thought, The label on the unit say's Mitsubishi/daiya Heavy industries. Does this mean its from a seperate part of the mitsi empire than the one that makes the M Series. Sould have also said the fault codes i was getting was U57 E01, I am assuming this is a general outdoor fault code but cannot see this on any Mitsi list i have got.

    Any help would be appreciated.


    Regards

    Raymond
    Last edited by Latte; 27-05-2004 at 10:05 AM.



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Mitsi Problems

    Raymond, first item... the crankcase heater is energised when the compressor is OFF
    second item, I will try and check the Mitsi tech disks for further info.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Mitsi Problems

    Mitsubishi Electric and Mitsubishi Heavy Industries are complete different products.
    We have better experiences with Electric.

  4. #4
    Join Date
    Mar 2004
    Location
    UK
    Posts
    624
    Rep Power
    21

    Re: Mitsi Problems

    Hi Raymond any joy with the mitsi

    Ref the leak I,ve had quite a few problems with R407c as the molecules are smaller than that of ofn.

    R407c is R134a 52%
    R32 23%
    R125 25%
    Zeotropes

    I have not enjoyed working with it and I belief they are phasing it out and replacing it with

    R410a R32 50%
    R125 50%
    This I enjoy working with and have had no problems
    So far

    The glide is similar with the latter

    Regards bernard

  5. #5
    Join Date
    Jan 2003
    Location
    East Anglia
    Posts
    1,160
    Rep Power
    25

    Re: Mitsi Problems

    Hi Guys,
    Havn't been back yet, too busy running around doing stupid jobs for a certain customer. Plan is to go back, check ofn pressure, vac out and regas to see what's happening when in running mode.
    Normally just deal with mitsi-elec and don't have too many probs this is he first time i have run into Misi-heavy and so far not impresed

    Regards

    Raymond

  6. #6
    Join Date
    Feb 2004
    Location
    Australia
    Posts
    286
    Rep Power
    21

    Re: Mitsi Problems

    Raymond

    I've had problems in the past with the Heavy Industries kit-if it was Mitsubishi Electric I could be more certain. The best thing might be to speak to the technical support guy at 3D Air who distribute the Heavy Industries (I believe the controls etc are all different from the Electric ones). Let me know if you want his contact details.

    Regards
    James
    a problem shared is a problem halved

  7. #7
    Join Date
    Jan 2003
    Location
    East Anglia
    Posts
    1,160
    Rep Power
    25

    Re: Mitsi Problems

    Hi Iceman,
    All OK, Found v/small leak on main suction flare. vac'd out & regassed and working fine. I must admit, i also prefer Electric to Heavy Industries.

    regards

    Raymond

  8. #8
    Join Date
    Feb 2004
    Location
    Australia
    Posts
    286
    Rep Power
    21

    Re: Mitsi Problems

    Glad you found the problem. I also had a leak problem with one of their VRF systems at the start of Spring.
    a problem shared is a problem halved

  9. #9
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Mitsi Problems

    hi raymond,

    this little gadget is the ultimate connection.
    can be open and closed 100's of times and will never leak.

    cost less then all the work involved in repairing a leak.

    does wonders for your reputation.

    chemi

    picture can be seen here http://www.refrigeration-engineer.co...ead.php?t=1636

  10. #10
    Join Date
    Dec 2004
    Location
    manchester
    Posts
    95
    Rep Power
    20

    Re: Mitsi Problems

    for mitsi heavy indust advice get in touch with the uk distributor it is called 3d air i dont have the number ,look in your contractors handbook
    they are normally v helpful

Similar Threads

  1. Replies: 10
    Last Post: 18-03-2006, 07:35 PM
  2. Problems LG don't want you to know about
    By Andy W in forum Air Conditioning
    Replies: 11
    Last Post: 16-02-2006, 04:52 PM
  3. Oil return problems
    By Peter_1 in forum Industrial
    Replies: 37
    Last Post: 23-08-2004, 11:30 PM
  4. oil pressure problems on air dryer
    By edge in forum Trouble Shooting
    Replies: 1
    Last Post: 16-07-2002, 02:10 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •