17-04-2009, 12:17 AM #1
Dorin K40CC
I have a problem with a compressor Dorin K40CC that is the following one: He works very well but after the defrosting it enters in vacuum (-10psi) and delay more or less fifteen minutes to normalize… why?
-
17-04-2009, 01:27 AM #2
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,175
- Blog Entries
- 6
- Rep Power
- 36
Re: Dorin K40CC
What makes you think that problem is in the compressor?
-
17-04-2009, 09:05 AM #3
Re: Dorin K40CC
Of course Nike, the compressor pulls the vacuum!!
xexito, check your controlls.
-
18-04-2009, 03:03 AM #4
-
18-04-2009, 07:25 AM #5
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,175
- Blog Entries
- 6
- Rep Power
- 36
Re: Dorin K40CC
Very strange and impossible to believe for me without further clarifications.
If compressor pulls vacuum that indicate that compressor doing his task (pumping) and that somewhere before pressure measuring point (where vacuum is observed), is some obstruction to refrigerant flow, or there is not enough heat at evaporator.
So question is: exactly where in circuit did you measured vacuum?
Next question would be: did You changed refrigerant with new fresh one, when you changed compressor, or did you recovered old refrigerant using new filter-dryer (as should be the trade practice) in line at suction of recovery gear, or you simply pumped system refrigerant in to receiver?
During compressor replacement, did you changed existing filter dryer in system with new one, as should be trade practice?
Or, could you describe exactly, step by step, everything you done during change of compressor?Last edited by nike123; 18-04-2009 at 07:32 AM.
-
18-04-2009, 08:45 PM #6
Re: Dorin K40CC
Totally agree with nike123 if the compressor is pulliing a vaccum then its pumping and pulling fine and the fault is some where else in the system.
-
19-04-2009, 07:16 PM #7
Re: Dorin K40CC
xexito.
Hi I must admit your question is strange, because a Dorrin Compressor designated CC is for Air-conditioning applications?
Yet you mention a issue after defrost?
So is the equipment correctly sized for the application?
If it is then my instinct tells me that several things could of occurred prior to the exchange.
Did the thermostat or any solenoid valves just happen to get changed at the same time?
I would be looking for why the refrigerant supply to the evap and therefore controlling Suction pressure.
Was being restricted for this 15 Min's period?
I suspect an electrical control issue
or a faulty defrost termination stat.
Good luck and please let us know more!
Grizzly
-
19-04-2009, 09:21 PM #8
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,175
- Blog Entries
- 6
- Rep Power
- 36
-
20-04-2009, 10:11 PM #9
Re: Dorin K40CC
Had exactly the same problem Nike and even more then once and the problem was indeed related to the compressor.
There was so much moisture in the system that the mesh filter inside the service valve (Dorin has the same mesh filter as a DWM/Copeland) completely clogged with ice mixed with oil. The compressor then pulls vacuum a vacuum in its sump but on the service valve, you measure a high evaporating pressure.It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
-
21-04-2009, 09:03 AM #10
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,175
- Blog Entries
- 6
- Rep Power
- 36
Similar Threads
-
Copeland select 6
By Copman in forum Tools and CalculatorsReplies: 9Last Post: 27-05-2010, 09:01 PM -
Require Dorin Info Please
By dsp in forum CommercialReplies: 2Last Post: 10-10-2008, 10:35 AM -
Dorin Compressor re-gas amount
By desserts in forum Technical SpeculationsReplies: 5Last Post: 25-09-2008, 11:30 AM -
Dorin Semi hermetic Compressor
By Samarjit Sen in forum Industrial CompressorsReplies: 5Last Post: 02-07-2007, 04:06 PM -
Dorin Compressors
By wesmax in forum Chit Chat & Service StoriesReplies: 2Last Post: 24-03-2005, 05:57 AM