    Dorin K40CC



    I have a problem with a compressor Dorin K40CC that is the following one: He works very well but after the defrosting it enters in vacuum (-10psi) and delay more or less fifteen minutes to normalize… why?



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: Dorin K40CC

    What makes you think that problem is in the compressor?

  3. #3
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: Dorin K40CC

    Of course Nike, the compressor pulls the vacuum!!


    xexito, check your controlls.

  4. #4
    Join Date
    Feb 2007
    Location
    Portugal
    Posts
    5
    Rep Power
    0

    Re: Dorin K40CC

    Quote Originally Posted by xexito View Post
    I have a problem with a compressor Dorin K40CC that is the following one: He works very well but after the defrosting it enters in vacuum (-10psi) and delay more or less fifteen minutes to normalize… why?
    The problem is realy the compressor, because this same compressor was exchanged for a new and the problem no longer exists ...

  5. #5
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: Dorin K40CC

    Quote Originally Posted by xexito View Post
    The problem is realy the compressor, because this same compressor was exchanged for a new and the problem no longer exists ...
    Very strange and impossible to believe for me without further clarifications.
    If compressor pulls vacuum that indicate that compressor doing his task (pumping) and that somewhere before pressure measuring point (where vacuum is observed), is some obstruction to refrigerant flow, or there is not enough heat at evaporator.
    So question is: exactly where in circuit did you measured vacuum?
    Next question would be: did You changed refrigerant with new fresh one, when you changed compressor, or did you recovered old refrigerant using new filter-dryer (as should be the trade practice) in line at suction of recovery gear, or you simply pumped system refrigerant in to receiver?
    During compressor replacement, did you changed existing filter dryer in system with new one, as should be trade practice?
    Or, could you describe exactly, step by step, everything you done during change of compressor?
    Last edited by nike123; 18-04-2009 at 07:32 AM.

  6. #6
    Join Date
    Aug 2006
    Location
    England
    Posts
    495
    Rep Power
    21

    Re: Dorin K40CC

    Totally agree with nike123 if the compressor is pulliing a vaccum then its pumping and pulling fine and the fault is some where else in the system.

  7. #7
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,758
    Rep Power
    46

    Re: Dorin K40CC

    xexito.
    Hi I must admit your question is strange, because a Dorrin Compressor designated CC is for Air-conditioning applications?
    Yet you mention a issue after defrost?
    So is the equipment correctly sized for the application?

    If it is then my instinct tells me that several things could of occurred prior to the exchange.
    Did the thermostat or any solenoid valves just happen to get changed at the same time?
    I would be looking for why the refrigerant supply to the evap and therefore controlling Suction pressure.
    Was being restricted for this 15 Min's period?
    I suspect an electrical control issue
    or a faulty defrost termination stat.
    Good luck and please let us know more!
    Grizzly

  8. #8
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: Dorin K40CC

    Quote Originally Posted by Grizzly View Post
    xexito.
    Hi I must admit your question is strange, because a Dorrin Compressor designated CC is for Air-conditioning applications?
    CC mean that it has more powerful engine but compressor is same. Therefore, depending on condensation temperature and refrigerant it could work in range -40°C<Te<10°C while C is Te -5°C max.

  9. #9
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34

    Re: Dorin K40CC

    Had exactly the same problem Nike and even more then once and the problem was indeed related to the compressor.
    There was so much moisture in the system that the mesh filter inside the service valve (Dorin has the same mesh filter as a DWM/Copeland) completely clogged with ice mixed with oil. The compressor then pulls vacuum a vacuum in its sump but on the service valve, you measure a high evaporating pressure.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  10. #10
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: Dorin K40CC

    Quote Originally Posted by Peter_1 View Post
    Had exactly the same problem Nike and even more then once and the problem was indeed related to the compressor.
    There was so much moisture in the system that the mesh filter inside the service valve (Dorin has the same mesh filter as a DWM/Copeland) completely clogged with ice mixed with oil. The compressor then pulls vacuum a vacuum in its sump but on the service valve, you measure a high evaporating pressure.
    So, change of compressor would not solve the problem. New compressor comes with same mesh filter and if refrigerant and filter dryer is not changed, same problem will be occurring again.
    Therefore, that is not compressor problem.

Similar Threads

  1. Copeland select 6
    By Copman in forum Tools and Calculators
    Replies: 9
    Last Post: 27-05-2010, 09:01 PM
  2. Require Dorin Info Please
    By dsp in forum Commercial
    Replies: 2
    Last Post: 10-10-2008, 10:35 AM
  3. Dorin Compressor re-gas amount
    By desserts in forum Technical Speculations
    Replies: 5
    Last Post: 25-09-2008, 11:30 AM
  4. Dorin Semi hermetic Compressor
    By Samarjit Sen in forum Industrial Compressors
    Replies: 5
    Last Post: 02-07-2007, 04:06 PM
  5. Dorin Compressors
    By wesmax in forum Chit Chat & Service Stories
    Replies: 2
    Last Post: 24-03-2005, 05:57 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •