    Small 1/2ton R22 marine A/C problem



    Hi all,
    I am bench testing a Cruisair marine A/C,7000 Btu,R22,RGA5480EXC Tecumseh compressor,water cooled coaxial condenser.
    I got it for free as scrap unit,I repaired a leak,removing the 4 way valve for the reverse cycle and recharged by weight (10 Oz)
    I arranged a "bench test" to read both suction and discharge pressures,change the load on evaporator with warm air and/or vary the fan speed,vary the condensing temperature changing the water flow,read the compressor current and both inlet /outlet air temp.
    It seems to "works" but...I observed some "strange" things:
    as I had a too low suction pressure,55 psi,and both suction & discharge press. does not rise as espected increasing the load on evaporator (only the superheat have increased).The superheath was almost correct,about 15F.
    I then tried to slowly rise the condensing pressure at the "nominal value" for summer sea water temperature but only the discharge pressure increased,the suction rised only a little (1-2 psi) and when I got around 230 psi the suction pressure began quickly to descend at less than 30 psi.The compressor current has increased as espected,and little or no cold at all air output.
    Any explaination?
    What others tests could I do to check it?
    I also observed that at compressor starting the suction pressure stays very low (15-20 psi) for a long time,let says 3 to 5 minutes...is it normal?
    Sorry for bad English language.
    Ciao from Italy
    Marco



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Small 1/2ton R22 marine A/C problem

    What sort of expansion device is the system using?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Apr 2009
    Location
    Italy
    Posts
    8
    Rep Power
    0

    Re: Small 1/2ton R22 marine A/C problem

    Hi,
    sorry to forgot to mention it.
    It is capillary tube,and it is rather short,just 8 inch
    Marco

  4. #4
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Small 1/2ton R22 marine A/C problem

    Make all measurments and than post data here!
    http://www.refrigeration-engineer.co...30&postcount=1
    Last edited by nike123; 17-04-2009 at 08:09 AM.

  5. #5
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Small 1/2ton R22 marine A/C problem

    Sounds like you have a blocked capillary and or drier, more than likely moisture blocking outlet of capillary, Start again and change filter drier and evacuate system several time.

Similar Threads

  1. MFI AMP6855 defrost problem
    By gliderpilot47 in forum Domestic
    Replies: 4
    Last Post: 12-01-2011, 12:11 PM
  2. problem with GE air con power problem
    By Richie101 in forum Air Conditioning
    Replies: 6
    Last Post: 05-11-2009, 04:00 PM
  3. crazy 3rd-world idea: aircon from small fridge
    By lsemprini in forum Fundamentals
    Replies: 71
    Last Post: 29-05-2008, 01:10 AM
  4. Furance problem
    By ALONEI in forum Trouble Shooting
    Replies: 10
    Last Post: 14-05-2008, 11:32 AM
  5. r404a small water-cooled marine freezer
    By keithholstead in forum Refrigerants
    Replies: 3
    Last Post: 01-12-2007, 01:07 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •