    Chilled water make up tank


    Can anyone tell me what level a make up water tank should top itself up to? I've done very little on chilled water air con systems. It's currently set up to top itself up to about 10%, but the building sparky keeps wanting to set it to 35 or 50%.



  2. #2
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    66
    Posts
    10,136
    Rep Power
    41

    Re: Chilled water make up tank

    I am a bit confused as the why an electrician is telling you what the water level should be in a make up tank.

    The level should be whatever is required to ensure that no air is drawn into the system on initial pump start up unless the system connection is at the ideal balance point when the level will not change.
    Brian - Torquay, Devon, UK
    I have to stop saying "how stupid can you be?" to my co-workers.
    They're starting to take it as a challenge...

    BASIC MAINTENANCE. If it doesn't move and it should then use WD40. If it moves but it shouldn't then use Duct Tape.

Similar Threads

  1. Ice Bank Tank for Chilled Water
    By Samarjit Sen in forum Commercial
    Replies: 26
    Last Post: 31-10-2009, 10:18 AM
  2. Need Help with cold water tank design
    By ac_sheldon in forum Industrial
    Replies: 9
    Last Post: 22-11-2008, 12:24 AM
  3. Energy saving in Chilled water system
    By psrao in forum Tools and Calculators
    Replies: 5
    Last Post: 15-01-2008, 07:54 PM
  4. Building a wine cabinet
    By Rory in forum Technical Discussions
    Replies: 38
    Last Post: 13-07-2004, 08:28 PM
  5. chilled water storage tank!
    By dchatta in forum Technical Discussions
    Replies: 4
    Last Post: 24-05-2004, 04:23 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •