Results 1 to 4 of 4

Thread: water flow

  1. #1
    Join Date
    Mar 2009
    Location
    basra
    Posts
    25
    Rep Power
    0

    water flow



    hi all I need anequation to calculate the flow of chilled water for 1 TR (24000BTU) to air cooled water chiller,please.



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: water flow

    The equation is Q = m x c x dt

    Where:
    Q = Refrigerating capacity
    m = mass flow of hydraulic fluid
    c = specific heat capacity of hydraulic fluid
    dt = the temperature difference of the hydraulic fluid

    What water flow and return temperatures are you expecting, and will you be using glycol in the hydraulic fluid?

  3. #3
    Join Date
    Apr 2009
    Location
    Panacea, Florida
    Age
    87
    Posts
    76
    Rep Power
    16

    Re: water flow

    Sorry, but this is in IP units, as I am from the U.S.

    Frank is pointing out that the required gallons/minute depends on the desired temperature drop of the chilled water temperature. General practice is to design for 10 degrees F. Therefore, the formula in IP units is:

    gallons/minute/ton = 12,000BTU/hr*(1/delta T)*gal/lb*(lb*degF/Btu)[specific heat]*hr/min

    For water, and 10 degrees F delta T, the result will be 2.4 gpm/ton

  4. #4
    Join Date
    Apr 2009
    Location
    Panacea, Florida
    Age
    87
    Posts
    76
    Rep Power
    16

    Re: water flow

    Frank is pointing out that the required gallons/minute depends on the desired temperature drop of the chilled water temperature. General practice is to design for 10 degrees F. Therefore, the formula in IP units is:

    Sorry, but this is in IP units, as I am from the U.S.

    gallons/minute/ton = 12,000BTU/hr*(1/delta T)*gal/lb*(lb*degF/Btu)[specific heat]*hr/min

    For water, and 10 degrees F delta T, the result will be 2.4 gpm/ton

Similar Threads

  1. Hoshizaki Ice Maker
    By Abe in forum Legal-Business-Marketing
    Replies: 19
    Last Post: 01-05-2010, 03:27 AM
  2. York Chiller evap water flow direction
    By mechillers in forum Technical Discussions
    Replies: 6
    Last Post: 30-03-2009, 05:37 PM
  3. Water Chiller High Water Flow
    By assadp in forum Fundamentals
    Replies: 15
    Last Post: 22-05-2008, 06:41 PM
  4. Water Flow Meter
    By puddleboy3 in forum Commercial
    Replies: 5
    Last Post: 12-07-2007, 07:43 PM
  5. Building a wine cabinet
    By Rory in forum Technical Discussions
    Replies: 38
    Last Post: 13-07-2004, 08:28 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •