    hi all I need anequation to calculate the flow of chilled water for 1 TR (24000BTU) to air cooled water chiller,please.
    Oct 2001
    Nottingham UK
    5,667
    Re: water flow
    The equation is Q = m x c x dt
    Where:
    Q = Refrigerating capacity
    m = mass flow of hydraulic fluid
    c = specific heat capacity of hydraulic fluid
    dt = the temperature difference of the hydraulic fluid
    What water flow and return temperatures are you expecting, and will you be using glycol in the hydraulic fluid?
    Apr 2009
    Panacea, Florida
    87
    Re: water flow
    Sorry, but this is in IP units, as I am from the U.S.
    Frank is pointing out that the required gallons/minute depends on the desired temperature drop of the chilled water temperature. General practice is to design for 10 degrees F. Therefore, the formula in IP units is:
    gallons/minute/ton = 12,000BTU/hr*(1/delta T)*gal/lb*(lb*degF/Btu)[specific heat]*hr/min
    For water, and 10 degrees F delta T, the result will be 2.4 gpm/ton