water flow
hi all I need anequation to calculate the flow of chilled water for 1 TR (24000BTU) to air cooled water chiller,please.
-
15-04-2009, 02:13 PM #2
Re: water flow
The equation is Q = m x c x dt
Where:
Q = Refrigerating capacity
m = mass flow of hydraulic fluid
c = specific heat capacity of hydraulic fluid
dt = the temperature difference of the hydraulic fluid
What water flow and return temperatures are you expecting, and will you be using glycol in the hydraulic fluid?
-
15-04-2009, 07:39 PM #3
Re: water flow
Sorry, but this is in IP units, as I am from the U.S.
Frank is pointing out that the required gallons/minute depends on the desired temperature drop of the chilled water temperature. General practice is to design for 10 degrees F. Therefore, the formula in IP units is:
gallons/minute/ton = 12,000BTU/hr*(1/delta T)*gal/lb*(lb*degF/Btu)[specific heat]*hr/min
For water, and 10 degrees F delta T, the result will be 2.4 gpm/ton
-
15-04-2009, 07:42 PM #4
Re: water flow
Frank is pointing out that the required gallons/minute depends on the desired temperature drop of the chilled water temperature. General practice is to design for 10 degrees F. Therefore, the formula in IP units is:
Sorry, but this is in IP units, as I am from the U.S.
gallons/minute/ton = 12,000BTU/hr*(1/delta T)*gal/lb*(lb*degF/Btu)[specific heat]*hr/min
For water, and 10 degrees F delta T, the result will be 2.4 gpm/ton
Similar Threads
-
Hoshizaki Ice Maker
By Abe in forum Legal-Business-MarketingReplies: 19Last Post: 01-05-2010, 03:27 AM -
York Chiller evap water flow direction
By mechillers in forum Technical DiscussionsReplies: 6Last Post: 30-03-2009, 05:37 PM -
Water Chiller High Water Flow
By assadp in forum FundamentalsReplies: 15Last Post: 22-05-2008, 06:41 PM -
Water Flow Meter
By puddleboy3 in forum CommercialReplies: 5Last Post: 12-07-2007, 07:43 PM -
Building a wine cabinet
By Rory in forum Technical DiscussionsReplies: 38Last Post: 13-07-2004, 08:28 PM