    Multistack heat pump



    Anyone have any problems with Multistack MS25 10/15 2HIR units? Have a problem with it cycling normally on (30 seconds in cooling, then switching into heat) then ever so often, it seems as if the reversing valve begins to modulate back into cooling, which can cause discharge to spike and trip on HPS. The relay is not chattering, no control related issue which seems to be causing this-seems to be mechanically at fault, though the valve in this unit was just replaced. Wondering if the reversing valve could be effected by a slug of oil or not-when the valve was replaced, there was a significant amount of oil in it.



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Multistack heat pump

    Could be...

    Is the refrigerant charge correct? Low pressure can cause poor operation of the valve.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    May 2006
    Location
    USA
    Age
    58
    Posts
    14
    Rep Power
    0

    Re: Multistack heat pump

    Brian-
    You're absolutely right-a low charge can give you a high pressure fault.(how anti-everything we've learned is that?)
    The charge is weighed in per Multistack. Our latest part of the puzzle is this: I have to go back out to the job and look to see how cap tubes common to the pilot activated reversing valve are tied in; if they tie from above the common line, we may be seeing an oil slug causing valve malfunction-below the line, maybe not.I'll let you know how this one turns out-
    Will

  4. #4
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Multistack heat pump

    I would first change solenoid coil. Or if you have this.
    What was problem with old valve? Did you changed coil when you changed valve.
    Last edited by nike123; 17-04-2009 at 10:07 AM.

Similar Threads

  1. Capacity control
    By sparrow in forum Training
    Replies: 44
    Last Post: 18-01-2010, 07:49 PM
  2. DIY heat pump 12kW
    By kimusabi in forum Fundamentals
    Replies: 11
    Last Post: 17-10-2009, 07:50 PM
  3. Pool heat pump water side diagram
    By nike123 in forum Heat Pumps
    Replies: 23
    Last Post: 22-03-2009, 07:42 PM
  4. frostles heat pump
    By Lc_shi in forum New Technologies
    Replies: 27
    Last Post: 31-03-2008, 07:53 AM
  5. Domestic VRF heat pump?
    By electronicsuk in forum Heat Pumps
    Replies: 8
    Last Post: 30-10-2007, 07:53 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •