    Undercharged and Overcharged Symptoms



    Hello all, i have just recenlty got a job as a trainee refrigeration engineer in Manchester, England. I just wanted to know, what the symptoms are for a Undercharged and a Overcharged System.. ??



  2. #2
    Hussain09's Avatar
    Hussain09 Guest

    Re: Undercharged and Overcharged Symptoms

    Hey Oscar, when a refrigeration system is overcharged, the compressor does tend to make loud (louder than normal) squelching noise..

    Hope this hepls

  3. #3
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,697
    Rep Power
    46

    Re: Undercharged and Overcharged Symptoms

    Hi Oscar.

    Here goes!
    Overcharged…
    1) Excessive subcooling at condenser outlet.
    2) Tripped on High Pressure Cut-out.
    3) High suction pressure with Low Suction Superheat.
    4) High delivery gauge reading with Normal superheat readings
    5) Low Delivery Gauge reading with low superheat
    6) Power absorbed by Compressor High

    Undercharged…
    1) Cut-out on L.P.
    2) Low Suction Pressure with High Suction superheat
    3) Low Discharge Pressure with High superheat
    4) Power absorbed by Compressor Low
    5) Comp shut down on L.P.

    The above is a guideline and not an complete list!
    Good Luck Grizzly

  4. #4
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Undercharged and Overcharged Symptoms

    Insufficient airflow through either coil will alter the refrigerant side symptoms, making troubleshooting extremely difficult. Always check for airflow problems first.

  5. #5
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,697
    Rep Power
    46

    Re: Undercharged and Overcharged Symptoms

    Quote Originally Posted by Gary View Post
    Insufficient airflow through either coil will alter the refrigerant side symptoms, making troubleshooting extremely difficult. Always check for airflow problems first.
    Good Point Gary, I have had many iced up comps and lp problems from frozen Cold store evaporator,
    Even when the fan has tripped because the melting ice on one of it's blades during defrost.
    Has bonded it to it's cowl tripping the fan motor overload!
    Grizzly

  6. #6
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Undercharged and Overcharged Symptoms


Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •