14-04-2009, 02:48 PM #1
Undercharged and Overcharged Symptoms
Hello all, i have just recenlty got a job as a trainee refrigeration engineer in Manchester, England. I just wanted to know, what the symptoms are for a Undercharged and a Overcharged System.. ??
-
14-04-2009, 04:14 PM #2
Re: Undercharged and Overcharged Symptoms
Hey Oscar, when a refrigeration system is overcharged, the compressor does tend to make loud (louder than normal) squelching noise..
Hope this hepls
-
14-04-2009, 05:26 PM #3
Re: Undercharged and Overcharged Symptoms
Hi Oscar.
Here goes!
Overcharged…
1) Excessive subcooling at condenser outlet.
2) Tripped on High Pressure Cut-out.
3) High suction pressure with Low Suction Superheat.
4) High delivery gauge reading with Normal superheat readings
5) Low Delivery Gauge reading with low superheat
6) Power absorbed by Compressor High
Undercharged…
1) Cut-out on L.P.
2) Low Suction Pressure with High Suction superheat
3) Low Discharge Pressure with High superheat
4) Power absorbed by Compressor Low
5) Comp shut down on L.P.
The above is a guideline and not an complete list!
Good Luck Grizzly
-
14-04-2009, 10:54 PM #4
Re: Undercharged and Overcharged Symptoms
Insufficient airflow through either coil will alter the refrigerant side symptoms, making troubleshooting extremely difficult. Always check for airflow problems first.
-
15-04-2009, 06:04 PM #5
Re: Undercharged and Overcharged Symptoms
-
17-04-2009, 02:10 PM #6
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: Undercharged and Overcharged Symptoms