    i recently job this field, now days i,m doing duty at york centrifugal chillier model YKDGHQ57CNF, 740 ton capicty , i want to learn about chillier , ok can any 1 help me, what is the SURGE , Explain thanks lot in advance



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,175
    Blog Entries
    6
    Rep Power
    36

    Re: what is surge in chiller

    By the very definition of Surge Drum (if that is what you asking), it is a vessel that is designed to provide a given volume or residence time for the fluid passing through.
    Last edited by nike123; 13-04-2009 at 06:03 PM.

  3. #3
    Join Date
    Jul 2008
    Location
    UK
    Age
    60
    Posts
    94
    Rep Power
    16

    Re: what is surge in chiller

    Quote Originally Posted by falibhatti View Post
    hi,
    i recently job this field, now days i,m doing duty at york centrifugal chillier model YKDGHQ57CNF, 740 ton capicty , i want to learn about chillier , ok can any 1 help me, what is the SURGE , Explain thanks lot in advance
    Try this
    http://www.mcquaybiz.com/mcquaybiz/l.../AG_31_002.pdf

    It is for Mcquay but a centrifugal never the less.

  4. #4
    Join Date
    Aug 2001
    Location
    UK
    Posts
    1,058
    Rep Power
    24

    Re: what is surge in chiller

    .

    In a centrifugal compressor, 'surge' is a name given to a dangerously unstable gas condition in the compressor and condenser.

    Put simply, it occurs when the forward compression thrust of gases in the compressor wheel falls below the critical velocity of the gas to flow forward through the condenser.

    When this happens, the pressure in the condenser is greater than the tip pressure of the compressor wheel and gas flows backwards from the condenser into the compressor. This has the effect of slowing the compressor down. At the same time the current will increase.

    When the compressor is able to overcome the instability in gas flow, it flows forward to the condenser again, only to repeat the process. The repeating cycle can occur rapidly, several times a minute.

    It is unmistakable when it is happening - you cannot mistake it.

    First, the compressor will make a sound as if it is speeding up and slowing down (which is what is happening).

    Second, the compressor current draw (amperage) will start to increase and decrease.

    Thirdly and finally, the compressor thrust assembly and bearings may become damaged and cause further damage to the gearbox.

    Excessive pressures in the condenser may rupture the safety disc or blow the relief valve.

    This is a condition that you don't want and usually indicates compressor loading and/or condensing problems.

    .

  5. #5
    Join Date
    Jun 2008
    Location
    u.a.e
    Posts
    4
    Rep Power
    0

    Re: what is surge in chiller

    can u explain me wat is delta p p ,

  6. #6
    Join Date
    Aug 2001
    Location
    UK
    Posts
    1,058
    Rep Power
    24

    Re: what is surge in chiller

    .

    Delta P = pressure difference, Delta T = Temperature difference.

    Usually the pressures or temperature differences entering and leaving a heat exchanger or vessel.


    .

  7. #7
    gary cato's Avatar
    gary cato Guest

    Re: what is surge in chiller

    surge is gas reversal from condenser high pressure through wheel into evaporator. this is caused more lift than the compressor was designed for. eg. high condenser, low load conditions,or incorrect charge.

  8. #8
    cool_waves2001's Avatar
    cool_waves2001 Guest

    Re: what is surge in chiller

    Quote Originally Posted by Argus View Post
    .

    In a centrifugal compressor, 'surge' is a name given to a dangerously unstable gas condition in the compressor and condenser.

    Put simply, it occurs when the forward compression thrust of gases in the compressor wheel falls below the critical velocity of the gas to flow forward through the condenser.

    When this happens, the pressure in the condenser is greater than the tip pressure of the compressor wheel and gas flows backwards from the condenser into the compressor. This has the effect of slowing the compressor down. At the same time the current will increase.

    When the compressor is able to overcome the instability in gas flow, it flows forward to the condenser again, only to repeat the process. The repeating cycle can occur rapidly, several times a minute.

    It is unmistakable when it is happening - you cannot mistake it.

    First, the compressor will make a sound as if it is speeding up and slowing down (which is what is happening).

    Second, the compressor current draw (amperage) will start to increase and decrease.

    Thirdly and finally, the compressor thrust assembly and bearings may become damaged and cause further damage to the gearbox.

    Excessive pressures in the condenser may rupture the safety disc or blow the relief valve.

    This is a condition that you don't want and usually indicates compressor loading and/or condensing problems.

    .
    thxs for information, i want 2 knwo more how it ill effect on thrust, bearings and gearbox.realy frm manydays i hv doubt i read it ur answer its realy wonderful,pls replay me

Similar Threads

  1. York Chiller problems
    By ingherrera in forum Commercial
    Replies: 18
    Last Post: 26-07-2011, 03:10 PM
  2. process chiller help
    By talon771 in forum Industrial
    Replies: 8
    Last Post: 12-01-2011, 09:42 PM
  3. Absorption Chiller VS Mech. Chiller
    By Intern in forum Industrial
    Replies: 20
    Last Post: 30-05-2009, 08:31 AM
  4. york chiller motor rotation error
    By cesarnino in forum Trouble Shooting
    Replies: 7
    Last Post: 13-12-2008, 04:43 PM
  5. Trane CVHE 450 R11 Centrifugal Chiller
    By albertjoseph in forum Air Conditioning
    Replies: 4
    Last Post: 06-10-2008, 03:23 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •