    250 Pcs Train Air conditions



    Dear Gentleman;

    I have 250 Pcs of Trane Air-condition 50Hz and in saudia Arabia we have 60 Hz ;If their is any converters in the market or solution to convert it please advise me .Or sale them in half price

    Best Regards



  2. #2
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: 250 Pcs Train Air conditions

    You don't need any converter.
    All the compressors and fan motors are made for 50 and 60 Hz.
    Take a close look at what is written on the compressors and other motors.

  3. #3
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    52
    Posts
    2,554
    Rep Power
    24

    Re: 250 Pcs Train Air conditions

    Yes, but the MRA must be reduced accordingly, to keep the max power input the same. That is the MRA @ 60Hz is 5/6ths of the MRA @ 50Hz

Similar Threads

  1. Operating Evaporative-Condensers in Extreme Winter Conditions.
    By stepperider in forum System Optimization
    Replies: 20
    Last Post: 29-07-2009, 09:35 PM
  2. fan speed control for air conditions
    By makis82 in forum Electrical
    Replies: 0
    Last Post: 03-12-2008, 09:07 AM
  3. Climatic conditions
    By nh3simman in forum Air Conditioning
    Replies: 2
    Last Post: 27-10-2008, 11:30 AM
  4. Chart for the "whys of conditions?
    By frankiee in forum Fundamentals
    Replies: 5
    Last Post: 30-04-2006, 09:26 PM
  5. Leaving conditions of DX HELP REQUIRED!!!
    By abbasi in forum Fundamentals
    Replies: 8
    Last Post: 24-08-2005, 09:19 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •