    cooling tower winter operation



    Hi sirs

    How to deal with the icing problem while cooling tower need to run at winter time? thx!

    rgds
    LC


    I hear...I forget;I see...I remember;I do...I understand

  2. #2
    Join Date
    Dec 2008
    Location
    UAE
    Age
    42
    Posts
    171
    Rep Power
    16

    Re: cooling tower winter operation

    Dear ,

    Please let me know what ambient temp you are talking about? Also is there a possibility to recirculate the Water with ambient cooling and bypassing the Cooling tower.

    Thanks
    Amit

  3. #3
    Join Date
    Dec 2004
    Location
    Weihai,China
    Posts
    800
    Rep Power
    20

    Re: cooling tower winter operation

    thanks

    It's -15C ambient temperature.
    I hear...I forget;I see...I remember;I do...I understand

  4. #4
    Join Date
    Dec 2008
    Location
    UAE
    Age
    42
    Posts
    171
    Rep Power
    16

    Re: cooling tower winter operation

    What i feel that when you are working in -15C then you need a Heat pump hence to heat the controlled ambient.Now this heat pump is need some heat load, which you want to give through Cooling tower water.
    Now there is only possibilty is that you mix some hot water to the water coming from your Heat Pump and then you wont face that prob.

    Please reply if u r satisfied.
    thanks
    amit

  5. #5
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: cooling tower winter operation

    The few cooling towers we have all have build-in electrical heaters. As soon temperature drops below 1°C, pump is started and no fans. If water temperature of the water measured at the inlet drops below 1°C, the heaters comes up. As soon there's load, water temperature increases and heaters shuts off.
    Heaters shut off at 3°C. Second redundant thermostat set at 0°C with a timer and a warning light to warn the user that there's something wrong with the heating.
    The outside steel pipes are also traced and wrapped in Armaflex.
    Your first step in capacity control is only pumps Lc? Then pumps and first speed of fans and then second speed of fans?
    At very low ambients - which we haven't here - you also could control speed of the pump.
    As long as the water is circulating, it may go even somewhat below freezing point.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  6. #6
    Join Date
    Jun 2008
    Location
    India
    Age
    56
    Posts
    64
    Rep Power
    16

    Re: cooling tower winter operation

    This thread is interesting to read...

    Is water-to-air heat pump a good option? Because water system cannot run below 0C. Is it a common practice to add glycol or some anti-freeze
    agent to take care of low winter temperatures?

  7. #7
    Join Date
    Dec 2008
    Location
    UAE
    Age
    42
    Posts
    171
    Rep Power
    16

    Re: cooling tower winter operation

    Dear I dont know how much i am correct,

    But in spite of fixing the heaters on the cooling tower, cant we fix the heaters with eva and make the heat transfer more efficient also the heaters will be controlled based on the cooling requirement and ambient temp.
    Reply if it is possible.
    thanks
    amit

  8. #8
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: cooling tower winter operation

    Cooling Tower Operation In Freezing Weather

    Cooling towers with malfunctions can freeze during very cold weather. Typically, freezing starts at the corners of a cooling tower with a reduced or absent heat load. Increased freezing conditions can create growing volumes of ice, resulting in increased structural loads. During the winter, some sites continuously operate cooling towers with 40 °F (4 °C) water leaving the tower. Basin heaters, tower draindown, and other freeze protection methods are often employed in cold climates.

    • Do not operate the tower unattended.


    • Do not operate the tower without a heat load. This can include basin heaters and heat trace. Basin heaters maintain the temperature of the water in the tower pan at an acceptable level. Heat trace is a resistive element that runs along water pipes located in cold climates to prevent freezing.


    • Maintain design water flow rate over the fill.


    • Manipulate airflow to maintain water temperature above freezing point.

    http://en.wikipedia.org/wiki/Cooling_tower

    http://spxcooling.com/pdf/H-003B.pdf
    Last edited by nike123; 13-04-2009 at 07:54 AM.

  9. #9
    Join Date
    Jun 2008
    Location
    India
    Age
    56
    Posts
    64
    Rep Power
    16

    Re: cooling tower winter operation

    Thanks Nike!

    You are amazingly quick with your information and support!

  10. #10
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: cooling tower winter operation

    Quote Originally Posted by K.R.Iyer View Post
    This thread is interesting to read...

    Is water-to-air heat pump a good option? Because water system cannot run below 0C. Is it a common practice to add glycol or some anti-freeze
    agent to take care of low winter temperatures?

    It is common practice, but only on closed loop systems. Water towers could be closed loop (indirect) and open loop (open to atmosphere, direct) systems, and you cannot add glycol to open loop system.

  11. #11
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: cooling tower winter operation

    Quote Originally Posted by K.R.Iyer View Post
    Thanks Nike!

    You are amazingly quick with your information and support!
    Probably I should start making money of that skill.

  12. #12
    Join Date
    Dec 2008
    Location
    China
    Posts
    87
    Rep Power
    16

    Re: cooling tower winter operation

    I have some suggestions:
    (1)You can collect the water indoor, so when the ambient temperature is low, you stop the pump and all the water is indoor, there will not be freeing problem;
    (2)You may put heater in your outdoor water collector, when ambient temperature is low, you can turn on the heaters.

  13. #13
    Join Date
    Aug 2008
    Location
    Englewood, CO
    Posts
    23
    Rep Power
    0

    Re: cooling tower winter operation

    There are a lot of good suggestions in this thread but I believe there a few misconceptions about sump heaters.
    Their sole purpose is to protect the sump against freeze up. Typically sized at 2-3KW each, they don't add much heat. With just the pump on, more heat would likely be removed from the water that a heater would add.
    Check the cooling tower manufacturer's wiring diagram- It will show the sump heater interlocked with the pump and fan. Both must be 'off' for the heater to be enabled.
    All the heater has to do is prevent basin ice from getting 'solid' thereby protecting the sump from the ice expanding before it freezes.
    Bottom line... Don't expect sump heaters to significantly offset the heat rejection of an operating cooling tower.

Similar Threads

  1. Compressor loading, cooling, and range of operation.
    By Air duster in forum Fundamentals
    Replies: 10
    Last Post: 02-04-2008, 08:39 AM
  2. large refrigeration plant cooling tower issue
    By Lc_shi in forum New Technologies
    Replies: 4
    Last Post: 25-03-2007, 01:35 PM
  3. cooling tower without fillings
    By Lc_shi in forum Fundamentals
    Replies: 3
    Last Post: 27-12-2005, 12:55 AM
  4. Cooling tower evaporation, blowdown, makeup and cycles
    By miltbeychok in forum Industrial
    Replies: 5
    Last Post: 14-10-2005, 06:34 PM
  5. Cooling tower evaporation, blowdown, makeup and cycles
    By miltbeychok in forum Fundamentals
    Replies: 0
    Last Post: 13-10-2005, 05:14 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •