    chilled water storage tank!



    can any body explain the basis for a chilled water storage tank in a packaged chilling plant ? what's the reason for keeping partition in it ( a hot well and acold well )?


    dchatta



  2. #2
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: chilled water storage tank!

    hi dchatta,

    water entering from the plant to the hot well, from there,into the the coolind unit and back to the cold well. from there, cold water supply is entering the plant.

    it saves two tanks that are connected with a pipe that does the same.

    in these systems a mixing valve should be used to save energy.


    chemi

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: chilled water storage tank!

    The water tank is also used to ensure sufficient load on the machine. The manufacturer has designed it to cool down a specific quantity of water but cannot be sure of the capacity of the pipework system. By having a storage tank it reduces the chances of the machine hunting due to reduced load.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24

    Re: chilled water storage tank!

    Hi
    a buffer tank is usually fitted to allow for a ten minute delay in restarting the compressor (nominal 6 starts per hour) and to handle peak loading. The tank is split warm return cold suply and usually set up with primary, evaporator pump and secondary service pump, with the evaporator pump being nominally 10% higher in flow rate than the service pump to allow for spill over from the cold to hot side only, so that only cooled water is supplied to the process.
    Kind Regards. Andy

  5. #5
    Join Date
    Apr 2004
    Location
    India
    Age
    45
    Posts
    7
    Rep Power
    0

    Re: chilled water storage tank!

    10x for reply,
    ur reply has cleared off many doubts

    but how are the various tank sizes decided ? is there some thumb rule for it , as like we have for condenser cooling water: 3 GPM per TR.

    and how do we calculate flow rate for GLYCOL mixtures ?
    what should be the criteria for selecting the pump for glycol(mixture) supply pump. do we have a thumb rule here also ...


    Dchatta
    Last edited by dchatta; 24-05-2004 at 04:58 PM.

Similar Threads

  1. Do I need a chilled water buffer vessel
    By Consultant in forum Commercial
    Replies: 32
    Last Post: 02-03-2011, 09:40 AM
  2. pure water from air
    By Lc_shi in forum New Technologies
    Replies: 32
    Last Post: 26-02-2009, 12:25 PM
  3. Building a wine cabinet
    By Rory in forum Technical Discussions
    Replies: 38
    Last Post: 13-07-2004, 08:28 PM
  4. Refrigerant vs Chilled Water
    By baker in forum Air Conditioning
    Replies: 4
    Last Post: 16-01-2004, 02:17 PM
  5. chilled water PHE
    By priti in forum Trouble Shooting
    Replies: 1
    Last Post: 31-07-2002, 08:25 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •