22-05-2004, 08:22 AM #1
chilled water storage tank!
can any body explain the basis for a chilled water storage tank in a packaged chilling plant ? what's the reason for keeping partition in it ( a hot well and acold well )?
dchatta
-
22-05-2004, 09:19 AM #2
Re: chilled water storage tank!
hi dchatta,
water entering from the plant to the hot well, from there,into the the coolind unit and back to the cold well. from there, cold water supply is entering the plant.
it saves two tanks that are connected with a pipe that does the same.
in these systems a mixing valve should be used to save energy.
chemi
-
23-05-2004, 11:24 PM #3
Re: chilled water storage tank!
The water tank is also used to ensure sufficient load on the machine. The manufacturer has designed it to cool down a specific quantity of water but cannot be sure of the capacity of the pipework system. By having a storage tank it reduces the chances of the machine hunting due to reduced load.
Brian - Newton Abbot, Devon, UK
Retired March 2015
-
23-05-2004, 11:35 PM #4
Re: chilled water storage tank!
Hi
a buffer tank is usually fitted to allow for a ten minute delay in restarting the compressor (nominal 6 starts per hour) and to handle peak loading. The tank is split warm return cold suply and usually set up with primary, evaporator pump and secondary service pump, with the evaporator pump being nominally 10% higher in flow rate than the service pump to allow for spill over from the cold to hot side only, so that only cooled water is supplied to the process.
Kind Regards. Andy
-
24-05-2004, 04:23 PM #5
Re: chilled water storage tank!
10x for reply,
ur reply has cleared off many doubts
but how are the various tank sizes decided ? is there some thumb rule for it , as like we have for condenser cooling water: 3 GPM per TR.
and how do we calculate flow rate for GLYCOL mixtures ?
what should be the criteria for selecting the pump for glycol(mixture) supply pump. do we have a thumb rule here also ...
DchattaLast edited by dchatta; 24-05-2004 at 04:58 PM.
Similar Threads
-
Do I need a chilled water buffer vessel
By Consultant in forum CommercialReplies: 32Last Post: 02-03-2011, 09:40 AM -
pure water from air
By Lc_shi in forum New TechnologiesReplies: 32Last Post: 26-02-2009, 12:25 PM -
Building a wine cabinet
By Rory in forum Technical DiscussionsReplies: 38Last Post: 13-07-2004, 08:28 PM -
Refrigerant vs Chilled Water
By baker in forum Air ConditioningReplies: 4Last Post: 16-01-2004, 02:17 PM -
chilled water PHE
By priti in forum Trouble ShootingReplies: 1Last Post: 31-07-2002, 08:25 PM