Results 1 to 8 of 8
Thread: Moisture in system
08-04-2009, 03:41 PM #1
Moisture in system
Hi guys i have been called to look at a Daikin 3MXS52E with three interior units off it. It has been installed for approx 10 months. An E6 error code has come up and i recently had the Daikin technician visit the property.
He has put in down to moisture in the system and it is not a warranty issue.
I would appreciate some info on the procedure of getting the moisture out of the system please.
08-04-2009, 04:05 PM #2
Re: Moisture in system
Erm! How long have you been an a/c engineer?
Try a triple evacuation or deep vacuum search within the forum or google it!
E6 Is listed in the details I have, as Outdoor Compressor lock / startup error
or lock / over-current.
Sounds to me as if there is an issue with the compressor!
GrizzlyLast edited by Brian_UK; 08-04-2009 at 07:13 PM.
08-04-2009, 04:48 PM #3
Daikin probably means "there was moisture in the system and now the compressor is f....d up". If this is the case, triple evacuation is no use and would not help restarting the compressor.
08-04-2009, 04:57 PM #4
Reclaim
Vaccum x 3 with nitrogen triple vac etc
Large 2 way HP drier in expansion line
run for a day, change
run for a week, change
run for a month -change or remove
How did he diagnose moisture anyway??
08-04-2009, 05:41 PM #5
08-04-2009, 05:58 PM #6
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
I would not do any recovery or drying of system before samples of oil and refrigerant are collected in manner that they are suitable for evidence and later analyze.
If he did not measured moisture content and sampled oil, how he could tell that is not warranty covered?
Also, moisture could be product of oil decomposition because high oil temperature and that could be because of some other fault in system, in which case that does not exclude warranty.Last edited by nike123; 08-04-2009 at 06:02 PM.
08-04-2009, 06:01 PM #7
08-04-2009, 06:15 PM #8
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Another taught!
If system is commissioned by authorized installer, then moisture in system cannot be reason for avoiding warranty repair since user is not responsible for faulty instalation.
Troubleshooting for Daikin Aircon CTK25FVEN
By JCTK in forum Air ConditioningReplies: 19Last Post: 05-06-2010, 07:18 PM -
CARE refigerants by BOC
By dogma in forum RefrigerantsReplies: 8Last Post: 23-03-2010, 12:39 PM -
How an expansion tank works?
By Raadster in forum FundamentalsReplies: 6Last Post: 25-07-2008, 02:25 PM -
dakin e3 code
By coolflow in forum Air ConditioningReplies: 2Last Post: 19-07-2008, 09:24 AM -
Automotive A/C Vent Temp Range vs System
By Don Browney in forum Air ConditioningReplies: 1Last Post: 15-05-2002, 06:19 AM