    Moisture in system



    Hi guys i have been called to look at a Daikin 3MXS52E with three interior units off it. It has been installed for approx 10 months. An E6 error code has come up and i recently had the Daikin technician visit the property.

    He has put in down to moisture in the system and it is not a warranty issue.

    I would appreciate some info on the procedure of getting the moisture out of the system please.



  2. #2
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,697
    Rep Power
    46

    Re: Moisture in system

    Quote Originally Posted by Debonair Spain View Post
    Hi guys i have been called to look at a Daikin 3MXS52E with three interior units off it. It has been installed for approx 10 months. An E6 error code has come up and i recently had the Daikin technician visit the property.

    He has put in down to moisture in the system and it is not a warranty issue.

    I would appreciate some info on the procedure of getting the moisture out of the system please.
    Erm! How long have you been an a/c engineer?
    Try a triple evacuation or deep vacuum search within the forum or google it!

    E6 Is listed in the details I have, as Outdoor Compressor lock / startup error
    or lock / over-current.
    Sounds to me as if there is an issue with the compressor!
    Grizzly
    Last edited by Brian_UK; 08-04-2009 at 07:13 PM.

  3. #3
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Moisture in system

    Daikin probably means "there was moisture in the system and now the compressor is f....d up". If this is the case, triple evacuation is no use and would not help restarting the compressor.

  4. #4
    Join Date
    Jul 2008
    Location
    London
    Posts
    848
    Rep Power
    17

    Re: Moisture in system

    Reclaim
    Vaccum x 3 with nitrogen triple vac etc
    Large 2 way HP drier in expansion line
    run for a day, change
    run for a week, change
    run for a month -change or remove

    How did he diagnose moisture anyway??

  5. #5
    Join Date
    May 2008
    Location
    spain
    Age
    54
    Posts
    63
    Rep Power
    17

    Re: Moisture in system

    Quote Originally Posted by multisync View Post
    Reclaim
    Vaccum x 3 with nitrogen triple vac etc
    Large 2 way HP drier in expansion line
    run for a day, change
    run for a week, change
    run for a month -change or remove

    How did he diagnose moisture anyway??
    To be honest Multisync i have not had the chance to ask him as i have only just received the info from Daikin and now they are on holiday until Tuesday.

    But many thanks

  6. #6
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Moisture in system

    Quote Originally Posted by Debonair Spain View Post
    To be honest Multisync i have not had the chance to ask him as i have only just received the info from Daikin and now they are on holiday until Tuesday.

    But many thanks
    I would not do any recovery or drying of system before samples of oil and refrigerant are collected in manner that they are suitable for evidence and later analyze.
    If he did not measured moisture content and sampled oil, how he could tell that is not warranty covered?
    Also, moisture could be product of oil decomposition because high oil temperature and that could be because of some other fault in system, in which case that does not exclude warranty.
    Last edited by nike123; 08-04-2009 at 06:02 PM.

  7. #7
    Join Date
    May 2008
    Location
    spain
    Age
    54
    Posts
    63
    Rep Power
    17

    Re: Moisture in system

    Quote Originally Posted by nike123 View Post
    I would not do any recovery or drying of system before samples of oil and refrigerant are collected in manner that they are suitable for evidence and later analyze.
    If he did not measured moisture content and sampled oil, how he could tell that is not warranty covered?
    Thanks Nike123 this is food for thought.

  8. #8
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Moisture in system

    Another taught!
    If system is commissioned by authorized installer, then moisture in system cannot be reason for avoiding warranty repair since user is not responsible for faulty instalation.

Similar Threads

  1. Troubleshooting for Daikin Aircon CTK25FVEN
    By JCTK in forum Air Conditioning
    Replies: 19
    Last Post: 05-06-2010, 07:18 PM
  2. CARE refigerants by BOC
    By dogma in forum Refrigerants
    Replies: 8
    Last Post: 23-03-2010, 12:39 PM
  3. How an expansion tank works?
    By Raadster in forum Fundamentals
    Replies: 6
    Last Post: 25-07-2008, 02:25 PM
  4. dakin e3 code
    By coolflow in forum Air Conditioning
    Replies: 2
    Last Post: 19-07-2008, 09:24 AM
  5. Automotive A/C Vent Temp Range vs System
    By Don Browney in forum Air Conditioning
    Replies: 1
    Last Post: 15-05-2002, 06:19 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •