08-04-2009, 08:56 AM #1
temp controller prob
hi got a new custom who has a problem with a VDH alfa 75 temperature controller. showing E1 presuming probe fault. looked on internet only site related to VDH is JOONDALUP in australia. emailed but no reply does any one know dealer in uk to contact to get new probe
-
08-04-2009, 04:25 PM #2
Re: temp controller prob
Hi Inkymart.
Check out the attached as I think despite being for a Alpha 53 the codes and suggested remedies are the same?
Good Luck Grizzly
Had another look around and found this which is for the 75. Ther are other model which have the 75 suffix in their model number . So hopefully this is the correct one?
GrizzlyLast edited by Grizzly; 08-04-2009 at 05:21 PM.
-
09-04-2009, 07:39 AM #3
Re: temp controller prob
Hi INKYMART123
If it is the probe your best bet is to measure the resistance of thermister most are about 5k ohms or 10k ohms. You can buy one from your local electronics supplier. It will cost no more than A$5 when the controller company would charge sometimes over A$100. Then if it needs callibrating add a variable pot of 10% in series or parallel to suit.
-
09-04-2009, 02:32 PM #4
Re: temp controller prob
thanks for info guys saved me alot of time looking on net.
Similar Threads
-
First post, please be nice, prob with heat mode
By back2space in forum Air ConditioningReplies: 93Last Post: 28-06-2009, 09:18 PM -
Daikin VRV-S controller configuration
By mchild in forum Air ConditioningReplies: 1Last Post: 12-03-2009, 08:06 PM -
Temp over run with Daikin VRV-S
By mchild in forum Air ConditioningReplies: 21Last Post: 14-12-2008, 03:19 AM -
Daikin Controller
By mchild in forum Air ConditioningReplies: 11Last Post: 24-11-2008, 02:34 AM -
Compressor loading, cooling, and range of operation.
By Air duster in forum FundamentalsReplies: 10Last Post: 02-04-2008, 08:39 AM