Thread: Scroll problems

  1. #1
    Join Date
    May 2001
    Location
    Trinidad,West Indies
    Posts
    16
    Rep Power
    0

    Thumbs up



    Hi guys, I'm new to this forum but I think it's a very informative site. I would like to get some feedback on the reliability and problems of scroll compressors.Recently we have lost 4 scroll compressors due to what seems to be a lack of lubrication.These compressors were from different systems with no apparent "system" problems.



  2. #2
    Join Date
    Apr 2001
    Posts
    19
    Rep Power
    0

    Cool

    Check rotation.Read amps.If 3 phase,reverse phases.

  3. #3
    Join Date
    May 2001
    Location
    Trinidad,West Indies
    Posts
    16
    Rep Power
    0

    Thumbs up Scroll problems

    These systems were commissioned about 9 months ago and 2 out of 4 compressors failed after 5 months.The system is a York package Liquid chiller with 2 independant refrigerant circuits of 2 compressors each.When the system was started-up,the voltage,rotation,superheat,oil level,pressures etc. were verified.Also a voltage monitor with phase reversal protection was installed.What I found odd is that I had to add 2 gallons of oil to the system and the oil level remained low.Seems as the compressors were pumping the oil out. I am presently working on 2 York Scroll systems and it seems as the compressors are pumping the oil out.I have already added 3 gallons of oil to these systems and the oil level is still low. I have never had this problem with recips. unless its a system problem. I'm trying to find out if other techs. out there are having the same problem.

  4. #4
    Join Date
    Mar 2001
    Location
    St. Louis, MO
    Posts
    509
    Rep Power
    24
    Keep in mind that the oil you are adding to the system isn't disappearing..... the oil is likely residing in the chiller. An appropriate question to ask at this point is why the oil isn't returning back to the compressor.
    Prof Sporlan

  5. #5
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35
    I agree, Prof. It isn't that the oil is pumping out of the compressor. The problem is that it isn't returning. Adding oil to a system is almost always a mistake.

  6. #6
    Join Date
    May 2001
    Location
    Trinidad,West Indies
    Posts
    16
    Rep Power
    0

    Thumbs up

    Gary I agree with you and Prof. Sporlan where the oil can be leaving and not returning.What does not seem to make sense is the fact that this is a package chiller so there is no "external" piping to cause oil return problems. Also the load in the evaporator is not lower than normal.(the g.p.m. is running slightly higher than design). Is there a tendency for Scroll compressors to circulate more oil through the system than Recips.

  7. #7
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35
    I know of no particular tendency for scroll compressors to circulate more oil, and the fact that you keep adding more and it doesn't come back should tell you something.

    Designed by the manufacturer doesn't necessarily translate to perfect design, although they tend to learn from their mistakes. Perhaps you are witnessing some of their mistakes.

    I would want to look very closely at the suction line sizing/sloping/trapping, as well as the chiller barrel flow pattern. Ask yourself, "Where is the low spot that is trapping the oil, while the refrigerant flows above it".

    As the Prof points out, it hasn't disappeared, it is hiding somewhere.

  8. #8
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60
    Originally posted by Jai
    this is a package chiller so there is no "external" piping to cause oil return problems
    We had to change out a compressor on a Daikin packaged chiller during last summer. One team started and I had to finish the final connection and get it running again.

    Found a lack of gas flow due to the discharge line up to the TEV being full of oil.

    Problem appeared to be bad location causing high pressure trips during hot weather....probably pumped out the oil and killed the compressor that way.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  9. #9
    Join Date
    Apr 2001
    Location
    Tyler, Texas
    Age
    53
    Posts
    12
    Rep Power
    0
    Scroll losses!!

    First ckeck you line size.. Then ckeck your super heat back to the compressor.

    1. DId the compessor ground out!!
    2. Are slugging the compressor
    3. Are you starving the compressor.
    Preston Roy Powell
    www.thinkcool.net

  10. #10
    Join Date
    Feb 2001
    Location
    Tampa Florida
    Posts
    1,076
    Rep Power
    25
    [quote]Found a lack of gas flow due to the discharge line up to the TEV
    being full of oil. [\quote]
    Last edited by Dan; 26-06-2002 at 06:14 AM.

  11. #11
    Join Date
    Apr 2002
    Location
    Samoa
    Posts
    13
    Rep Power
    0
    One might expect some of the oils to come back to the compressor when it starts warm. Unless it is on 24 hr operation.You couls also check water flows etc.
    One of the intersting points here being raised also is putting in oils when you can't see it on the ground!!! or ceiling or anywhere.
    I have problems sometimes with some of our guys who believe if oil level is low it needs oil. As you all suggest step back and re focus.

  12. #12
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Scroll problems

    have you done acid test on each circuit ,were drier cores,contactors changed with new compressors,are the compressors short cycling,condenser coils clean,tev functioning correctly.mains problems on site???????????????

  13. #13
    Join Date
    Oct 2007
    Location
    Britain
    Posts
    220
    Rep Power
    17

    Re: Scroll problems

    You could try isolating one circuit to ensure compressors are running at 100% capacity which will ensure maximmum oil return, is there an oil return line from the evaporator?

    Cheers
    Tutto il Mondo e un Paese

  14. #14
    Join Date
    Oct 2007
    Location
    Britain
    Posts
    220
    Rep Power
    17

    Re: Scroll problems

    Just a thought, is there a water flow problem on that site, did they leave flow rate measurements on the commissioning sheets? If you post the model number one of the Yorkies might be able to give you more information.

    Cheers
    Tutto il Mondo e un Paese

Similar Threads

  1. Replies: 10
    Last Post: 18-03-2006, 07:35 PM
  2. Problems LG don't want you to know about
    By Andy W in forum Air Conditioning
    Replies: 11
    Last Post: 16-02-2006, 04:52 PM
  3. Oil return problems
    By Peter_1 in forum Industrial
    Replies: 37
    Last Post: 23-08-2004, 11:30 PM
  4. Scroll Compressor
    By dwallan in forum Commercial
    Replies: 1
    Last Post: 30-07-2001, 04:18 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •