Results 1 to 4 of 4
Thread: hunting???
-
17-05-2004, 11:58 AM #1
hunting???
Hi;
Iīm reading an english paper and i donīt understand the following:
Thermostatic expansion valve operation requiere condensing pressure control, to ensure a minimum pressure-difference over the expansion valve. Too low pressure-differences result in hunting.
What does hunting mean here??
Rgrds
-
17-05-2004, 02:43 PM #2
Re: hunting???
hi Friobernal,
hunting is a term used to identify the changes in refrigerant flow through the TEV.
it will open too much, allowing too much refrigerant into the evaporator and then close too much restricting the flow.
maintaining the condensing pressure high enough, will avoid hunting.
chemi
-
17-05-2004, 03:30 PM #3
Re: hunting???
-
18-05-2004, 02:00 PM #4
Re: hunting???
Friobernal
In this context it is term borrowed from the automotive industry that describes an oscillation encountered originally in a poorly adjusted engine timing system that allowed the carburettor to open and close. The engine would speed up and slow down rapidly.
Used in the context of a TEV it describes either a poorly sized evaporator / TEV combination or a defect in the TEV that allows it to adjust wildly ranging, from flooding to starving the coil. You will see it on your gauges as an oscillation in pressure. There are a number of things that can cause it.
One thing is certain - you don't want it!
Hope it helps.
________
TraverseLast edited by Argus; 07-02-2011 at 08:04 AM.
Similar Threads
-
Hunting Etc.
By subzero*psia in forum HobbiesReplies: 27Last Post: 19-09-2010, 01:40 PM -
job hunting
By neil sailes in forum Chit Chat & Service StoriesReplies: 19Last Post: 13-10-2005, 09:00 PM -
EXV Hunting
By Dan H in forum Trouble ShootingReplies: 11Last Post: 28-06-2005, 09:53 AM -
Job hunting...
By morpheas_24 in forum Chit Chat & Service StoriesReplies: 2Last Post: 17-06-2002, 11:07 AM -
Subcool and Superheat