    About 2 stage coil



    Hi,
    Would like to know 2 stage compressor coil which mark 1,2,3 and 7,8,9, is there any difference if i connect it 789 as first step in and 123 as second step in.

    Last week one of my customer 30hp 2 stage compressor burn down, i removed the coil which mark 123 as R,Y,B line (first step contactor) and 7,8,9 as RYB line (second step). Then, they passed me a secondhand 30hp coil without numbers but with 3 phase colour for both step.

    I checked both coil with same ohm, check contactor contact point and changed all the necessary things like oil, filter and etc.then fixed it back. When start both part running at 16-18amp, when it getting colder dropped to 14amp, next day i changed another filter everything running smoothly, but till evening the coil burn down again (first step coil).

    So would like to know 2 stage compressor coil which mark 1,2,3 and 7,8,9, is there any difference if i connect it 789 as first step in and 123 as second step in . ? I installed this system coming 4 years and this is the first time it burn down.



  2. #2
    Join Date
    Aug 2006
    Location
    England
    Posts
    495
    Rep Power
    21

    Re: About 2 stage coil

    hello mate if its standard 50/50 part wind it doesnt matter but if you have for example copeland awm=66/33 or Bwm=60/40, then you have to wire in the first contactor to the biggest half of winding ,otherwise it will burn out under load because it wont be able to get away. But also check if the second contactor is comming in after about a second,to make easy to check what windinds you have is ,50/50=same ohms reading across both sets of pins,and if you got the newer types of part winds the three pins with lowest ohms readings are the biggest halfs,they must be first step in

  3. #3
    Join Date
    Mar 2009
    Location
    Brunei
    Posts
    7
    Rep Power
    0

    Re: About 2 stage coil

    Hi GHAZ,
    Same ohms, carrier compressor. They bring me to have a look at the compressor where they get the coil, it's a 30hp carrier compressor but not 2 stage type. I don't see any amps difference when starting and running betw the 2 coil. So can you figure out what's the problem here?

    One more question, how to specify carrier compressor HP other than looking at the coil label?

  4. #4
    Join Date
    Aug 2006
    Location
    England
    Posts
    495
    Rep Power
    21

    Re: About 2 stage coil

    Hello mate if you give the correct model number of compound compressor and the one you took the coil out of and the stator core length of both,and i can then tell you the horsepower
    Last edited by GHAZ; 09-04-2009 at 08:28 PM.

Similar Threads

  1. Building a 3 stage cascade
    By NoL in forum CPU Overclockers
    Replies: 9
    Last Post: 27-03-2009, 08:42 PM
  2. Dont be shy, advice needed.
    By Sledge in forum Air Conditioning
    Replies: 9
    Last Post: 27-06-2007, 03:09 PM
  3. Single stage Vs 2 stage comp rack
    By Kevin Yeo in forum Supermarket Refrigeration
    Replies: 0
    Last Post: 01-02-2007, 03:05 PM
  4. Burst Coil
    By frank in forum Air Conditioning
    Replies: 13
    Last Post: 20-02-2005, 06:28 PM
  5. Article in ACH&R News
    By Gary in forum Fundamentals
    Replies: 8
    Last Post: 20-05-2003, 12:27 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •