    vertical oil separator or horizontal type?



    Vertical oil separator or horizontal oil separator, which type do you prefer?
    in my opinion that the larger machines are supplied to a vertical oil separator and the smaller ones are thorizontal type (ignoring the design conditions)
    but I was told that usually the vertical type is use in the smaller compressors (say swept volume below 5000m3/h)and horizontal is used in the larger ones.
    i know that the type and size of oil separator is determined by the design condition,but are there any rules for selecting a oil separator's type? for a big compressor which type is more common in your actual applications?

    thanks a lot

    cygbob



  2. #2
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,356
    Rep Power
    39

    Re: vertical oil separator or horizontal type?

    cygbob ,
    Does not matter as its usually to make package cheaper ( horizontal ).
    Horizontal is harder to work on the bigger the compressor in my opinion .

  3. #3
    Join Date
    Jan 2009
    Location
    INDIA
    Posts
    40
    Rep Power
    0

    Re: vertical oil separator or horizontal type?

    Quote Originally Posted by RANGER1 View Post
    cygbob ,
    Does not matter as its usually to make package cheaper ( horizontal ).
    Horizontal is harder to work on the bigger the compressor in my opinion .
    usually compressor is mounted over horizontal oil tank seperator which decreases the cost of package. This configuration helps to make the package more compact and samller in size.

  4. #4
    Join Date
    Aug 2006
    Location
    CHINA
    Posts
    29
    Rep Power
    0

    Re: vertical oil separator or horizontal type?

    Quote Originally Posted by RANGER1 View Post
    Horizontal is harder to work on the bigger the compressor in my opinion .
    Why?is it because of the stress caused by the heavy compressor and motor? or does it have the limitation of height for transport?
    i think Horizontal has a good performance

  5. #5
    Join Date
    Mar 2009
    Location
    U.S.A.
    Posts
    320
    Rep Power
    20

    Re: vertical oil separator or horizontal type?

    Performance wise, there's not much to discern these days.

    Design geometry: Fewer practical limitations on oil level, check valve locations and so on with a horizontal separator; and a big motored vertical separator package ends up with the machine mounted on heavy structural steel (which is $$$) and often, a collection of instrument tubing and similar above the machine. Pull the machine may require undoing a bunch of plumbing with a vertical Oil Sep.

    And a vertical tends to have a smaller foot print in the machine room. Often.
    But they can represent some design concerns where condensers are already only 4 to 9 feet above surface level.

    Small horizontal packages easy to work with; large packages need specialty access to install either way; and a large package with a horizontal separator is not as easy to work on for normal servicing as Ranger1 said....

    Although technically both represent confined spaces for coalescer replacement according to OSHA, on a small horizontal its ridiculous to presume anyone is going to get their feet off the ground. With a vertical, you got your feet off the ground before you access the manhole cover in most cases.

  6. #6
    Join Date
    Dec 2007
    Location
    iran
    Age
    45
    Posts
    36
    Rep Power
    0

    Re: vertical oil separator or horizontal type?

    large compressor is heavy and if it is mounted on horizental oil separator.the height of gravity mass is increased so stability will be ecreased and vibration will be increased

  7. #7
    Join Date
    Jan 2006
    Location
    Norway
    Posts
    1,044
    Blog Entries
    4
    Rep Power
    31

    Re: vertical oil separator or horizontal type?

    we use horizontal oil separators on all our compressor units (usually Howden), as they take less space, since the separator is bellow the compressor and motor, instead of adding another 2 feet to the length and another 7 feet to the height of the unit.


    the only thing to remember on horizontal oil separators where the motor and compressor is mounted on top is that the alignment has to be checked both when the unit is cold and when it's hot. This to ensure that they don't move out of alignment when the unit is warm.
    -Cheers-

    Tycho

Similar Threads

  1. breaker type?
    By tait71 in forum Electrical
    Replies: 24
    Last Post: 05-09-2010, 04:39 AM
  2. Replies: 11
    Last Post: 12-02-2009, 10:06 AM
  3. 410A guages which type?
    By N.Lewis in forum Tools and Calculators
    Replies: 6
    Last Post: 01-09-2008, 05:27 PM
  4. earth leakage
    By sid in forum Electrical
    Replies: 33
    Last Post: 11-07-2008, 07:58 PM
  5. Replies: 4
    Last Post: 11-05-2007, 02:15 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •