Hello
I was recently thinking about replacing my standard central heating with something less conventional like heat pump. My house is about 200m2 and I don't know how much power I would need to heat it in the winter. As far as I know, there are heat pumps from 10kW to 35kW ( solarusmax.com/pompyciepla.php ). Thank you in advance for any answer.
-
03-04-2009, 06:44 PM #2
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: Heat pump power
You need someone to do house heat loss calculation.
-
14-04-2009, 08:58 PM #3
Re: Heat pump power
Before you retrofit to a heat pump, there are a few things to consider, especially if you have long cold winters. First, heat pumps are not as efficient as a condensing gas furnace, which has a COP of nearly 1, even when the outdoor temperature is well below freezing. Electric heat pumps have a COP of 3 or more, but that is at 47 F, and is the ratio of btuh out to site btuh (site electric power) in. The actual efficiency is about 3.5 times less than 3, or less than 1, especially if the temperature is only 17 F. At 17F most heat pumps have a COP of about 2, or a fuel efficiency of .57. This is because the power plant supplying the electric power is much less efficient than a local furnace – usually only 30% or so. That’s why the cost of electricity per million Btu is generally about 3 times the cost of fossil fuel.
Second, heat pumps don’t generate much hot air. Since they are usually also summer cooling machines, the airflow across the coil is high relative to a furnace, so for a given capacity, heat pumps circulate colder air – on the order of 80 – 85 F – than furnaces which deliver nice warm air at 95 – 120 F. Also, the colder it gets, the more dependent on the “auxiliary” electric heat. That can warm the air, but at the expense of COP.
I live in Florida, and mostly specifiy heat pumps for my clients. If I practiced in Austria, I don’t think I would recommend heat pumps.
-
26-04-2009, 10:07 PM #4
Re: Heat pump power
It depends on the region you live in. Heat pumps will give good heat until the osa drops below 35F to 33F anything below this will cost you electricity for strip heating. It does have it's advantages in tropic areas or in areas (rural) where no NG gas is available.
Similar Threads
-
Capacity control
By sparrow in forum TrainingReplies: 44Last Post: 18-01-2010, 07:49 PM -
Some information on the aplication of suction gas/liquid line heat exchangers
By SteinarN in forum FundamentalsReplies: 5Last Post: 14-09-2009, 07:33 AM -
Pool heat pump water side diagram
By nike123 in forum Heat PumpsReplies: 23Last Post: 22-03-2009, 07:42 PM -
Heat transfer coefficient - Coolpack
By Graham in forum FundamentalsReplies: 10Last Post: 28-05-2008, 01:08 AM -
frostles heat pump
By Lc_shi in forum New TechnologiesReplies: 27Last Post: 31-03-2008, 07:53 AM