G'day
i have a carrier Chiller 30GB-210.940
Unique No. 30GB.210 OOO571
S/N 0697W09089
Unit has had a History of tripping HP on 30+(c) days
Pipework does not seem to distribute hot gas evenly and bottom horizontal coils do no work
anyone else had a similar problem chiller is about 12 years old
-
02-04-2009, 06:50 AM #2
Re: carrier chiller hp problems
Hi pobbo
Check the HP sensor callibration and superheat and subcooling - aim for about 10k subcooling. Also check comp current, ref charge, and obviosly condition of heat exchanger. If the heat exchanger is degraded reduce ref charge. Look for any modification on liquid line ie smaller drier fitted. Check the above with a good load.
-
02-04-2009, 09:38 PM #3
Re: carrier chiller hp problems
pobbo.
Welcome, I cannot really add much to Tesla's excellent advice.
Other than to ask what you mean by the following- "bottom horizontal coils do no work"
Is it because the fin condition has deteriorated so that there is poor flow through them?
Or they may be oil logged?
Damaged?
System overcharged?
Put me out of my misery, what is wrong with them.
If it is down to old age etc. I have resorted to the old lawn sprinkler trick!
Mind we don't suffer from water shortages as much over here.
Cheers Grizzly
Similar Threads
-
York Chiller problems
By ingherrera in forum CommercialReplies: 18Last Post: 26-07-2011, 03:10 PM -
MICROPROCESSOR DIAGNOSTICS/Differnces beteween TK/CTC
By REEFER-TEK in forum TransportReplies: 12Last Post: 27-03-2011, 04:12 AM -
Carrier 30XA Liquid chiller Problems
By Ed Burris in forum CommercialReplies: 7Last Post: 13-08-2010, 08:12 PM -
Carrier chiller basic board problem
By noushad123 in forum Trouble ShootingReplies: 25Last Post: 17-06-2010, 06:55 AM -
Carrier Chiller Help
By superswill in forum Trouble ShootingReplies: 7Last Post: 18-01-2007, 11:06 PM