Results 1 to 9 of 9
Thread: Carrier Chiller 30GX Error Code
01-04-2009, 05:54 AM #1
I am getting following error code in 30GX 160 TR and 190 TR : Error Code No. 303, 14, 55, 20 & 50. I don't carrier manual with me, can anyone please provide me the details of these errors and solution for rectifiying the problem.
01-04-2009, 06:57 PM #2
Re: Carrier Chiller 30GX Error Code
Have you tried the Carrier literature site.
http://eto.carrier.com/lit.asp
Scroll down the list for the 30GXBrian - Newton Abbot, Devon, UK
05-04-2009, 08:03 PM #3
303 hi press 55 no flow comp
10-04-2009, 05:45 PM #4
Unit tripping instantly while start up due to failure of oil pump on line
14-04-2009, 03:40 AM #5
hi well i thick that you has problem with the compressor board n can skip the board to do a test n i will give u most detail on the alarm code ok
21-10-2009, 11:37 PM #6
DEAR
20,50,14,303 THE ALARMS ARE NOT IN THE MANUAL WITH RESPECT ME I NEED 55 ALA ALARM ALARM YOU SAY THAT APPEARS IF THE DRIVER COMFORTLINK ALARM AS OTHER FACTORS 55 are CCP or the module is damaged.
22-10-2009, 10:02 PM #7
There are 3 versions of this chiller, can you describe the chiller display that will identify the version so we can point you in the right direction regarding the manual.
23-10-2009, 01:10 PM #8
14 Discharge pressure transducer failure, circuit A Measured signal = 0V dc Circuit A shut down Automatic Defective transducer, wiring fault
15 Discharge pressure transducer failure, circuit B Measured signal = 0V dc Circuit B shut down Automatic20 Oil pressure transducer failure, compressor B1 Measured signal = 0V dc Compressor B1 shut down Automatic Ditto3xx Defect compressor B1 See CPM subcodes below See CPM subcodes below Manual
if u mail me gill@gosheneng.co.il i will mail u the manual
07-03-2010, 02:57 AM #9
Hi goshen (Gill), Wondering if you could email me the full manual on the 30GX screw chiller. Greatly appreciated. My email address is in my details. Thanks again.
Carrier chiller basic board problem
By noushad123 in forum Trouble ShootingReplies: 25Last Post: 17-06-2010, 06:55 AM -
30GX Carrier screw compressor
By malik55 in forum Air ConditioningReplies: 9Last Post: 19-04-2009, 12:16 PM -
Carrier Chiller Help
By superswill in forum Trouble ShootingReplies: 7Last Post: 18-01-2007, 10:06 PM -
Carrier chiller oil migration
By lowtech in forum IndustrialReplies: 5Last Post: 30-04-2006, 04:11 PM