    Help using coolpack for cold room



    Hi I have a room being stored in a supermarket that is 3 x 2.5 x 2 and it will be storing meats. The ambient store temp is 20c. How can I utilise coolpack to make this calculation. I also would like to know what Tcool(h) means. Any help would be useful, this is for a college work and I just want to know if I using this program correctly. Thanks.



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Help using coolpack for cold room

    Have you tried the HELP files of Coolpack?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Apr 2008
    Location
    West Yorkshire
    Age
    42
    Posts
    62
    Rep Power
    17

    Re: Help using coolpack for cold room

    They don't tell you anything. I may have to do this manually.

  4. #4
    Join Date
    Feb 2008
    Location
    Norway
    Age
    57
    Posts
    446
    Rep Power
    17

    Re: Help using coolpack for cold room

    Tcool [h] means the time for the cool down of the warm products loaded into the cool room. "T" says it is time, "[h]" says the time is in hours.

  5. #5
    Join Date
    Apr 2008
    Location
    West Yorkshire
    Age
    42
    Posts
    62
    Rep Power
    17

    Re: Help using coolpack for cold room

    Quote Originally Posted by SteinarN View Post
    Tcool [h] means the time for the cool down of the warm products loaded into the cool room. "T" says it is time, "[h]" says the time is in hours.
    Ok, thanks.

  6. #6
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Help using coolpack for cold room

    Quote Originally Posted by W.Miller View Post
    They don't tell you anything. I may have to do this manually.
    This is from Help:Printing _Description of model_.pdf

    I think that description is good enough for average person.
    Last edited by nike123; 31-03-2009 at 10:18 AM.

  7. #7
    Join Date
    Apr 2008
    Location
    West Yorkshire
    Age
    42
    Posts
    62
    Rep Power
    17

    Re: Help using coolpack for cold room

    Sorry to be a pain, but does that mean if I wanted to cool meat down to -18 from 15c would I change the Tcool to 1 hour. Is that normal industry standard.

  8. #8
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Help using coolpack for cold room

    Quote Originally Posted by W.Miller View Post
    Sorry to be a pain, but does that mean if I wanted to cool meat down to -18 from 15c would I change the Tcool to 1 hour. Is that normal industry standard.
    Yes, that mean that, and not, that is not industry standard.
    For illustration purpose:
    http://www.meatupdate.csiro.au/data/Meat_93_24.pdf
    Last edited by nike123; 31-03-2009 at 02:25 PM.

  9. #9
    Join Date
    Feb 2008
    Location
    Norway
    Age
    57
    Posts
    446
    Rep Power
    17

    Re: Help using coolpack for cold room

    Quote Originally Posted by W.Miller View Post
    Sorry to be a pain, but does that mean if I wanted to cool meat down to -18 from 15c would I change the Tcool to 1 hour. Is that normal industry standard.
    I doubt 1 hour is industry standard.

    The actual cooling/freezing time is highly dependent of the air flow, the size of the meat pieces and whether it is packed or hanging free.

    If it is not a fast cooling/freezing room I would have set the Tcool to 24 hours and the set the quantity of products to load every day some 20 to 30 percent higher than the real quantity loaded into the room every day. Or alternatively set the real quantity and set a Tcool of 15 to 18 hours. This would give a reasonable spare capasity for defrosting.

  10. #10
    Join Date
    Apr 2008
    Location
    West Yorkshire
    Age
    42
    Posts
    62
    Rep Power
    17

    Re: Help using coolpack for cold room

    Ok after using cool pack I came up with these answers.

    (uncooked meat)
    Room size = 3 x 2.5 x 2
    Troom = 0c
    Rh = 85%
    Ambient = 23c
    Rh = 65%
    Acf = 9
    goods = 1000g
    Tin(c) = 17
    tcool = 15
    Persons = 1
    Work type = heavy
    Lights 100w/m2

    Now it says I need a maximum of 7.8 kw for the room stated.
    All I would like to know is 7.8kw enough for this space?

  11. #11
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Help using coolpack for cold room

    Quote Originally Posted by W.Miller View Post
    Ok after using cool pack I came up with these answers.

    (uncooked meat)
    Room size = 3 x 2.5 x 2
    Troom = 0c
    Rh = 85%
    Ambient = 23c
    Rh = 65%
    Acf = 9
    goods = 1000g
    Tin(c) = 17
    tcool = 15
    Persons = 1
    Work type = heavy
    Lights 100w/m2

    Now it says I need a maximum of 7.8 kw for the room stated.
    All I would like to know is 7.8kw enough for this space?
    For 1000g of goods in 15 hours, more than enough.

  12. #12
    Join Date
    Apr 2008
    Location
    West Yorkshire
    Age
    42
    Posts
    62
    Rep Power
    17

    Re: Help using coolpack for cold room

    Excellent I will add that calculation to my work and hopefully get a pass mark.

  13. #13
    Join Date
    Feb 2008
    Location
    Norway
    Age
    57
    Posts
    446
    Rep Power
    17

    Re: Help using coolpack for cold room

    What did you get as an average capasity requirement?

  14. #14
    Join Date
    Apr 2008
    Location
    West Yorkshire
    Age
    42
    Posts
    62
    Rep Power
    17

    Re: Help using coolpack for cold room

    I think it was around 3.7 kw.

  15. #15
    Join Date
    Feb 2008
    Location
    Norway
    Age
    57
    Posts
    446
    Rep Power
    17

    Re: Help using coolpack for cold room

    I would have used the average capasity requirement as this gives a reasonable spare capasity.

    The max capasity is the capasity needed to avoid the cool room temp increasing temporarily if the daily meat is put into the room all at once. This capasity requirement is also subjected to a number of aproximations in the coolpack program. A somewhat different number can be as correct as the coolpack number.
    Last edited by SteinarN; 01-04-2009 at 07:09 PM.

  16. #16
    Join Date
    Apr 2008
    Location
    West Yorkshire
    Age
    42
    Posts
    62
    Rep Power
    17

    Re: Help using coolpack for cold room

    Quote Originally Posted by SteinarN View Post
    I would have used the average capasity requirement as this gives a reasonable spare capasity.

    The max capasity is the capasity needed to avoid the cool room temp increasing temporarily if the daily meat is put into the room at once. This capasity requirement is also subjected to a number of aproximations in the coolpack program. A somewhat different number can be as correct as the coolpack number.
    Thanks I will take your advice.

  17. #17
    Join Date
    Apr 2008
    Location
    West Yorkshire
    Age
    42
    Posts
    62
    Rep Power
    17

    Re: Help using coolpack for cold room

    Quote Originally Posted by SteinarN View Post
    I would have used the average capasity requirement as this gives a reasonable spare capasity.

    The max capasity is the capasity needed to avoid the cool room temp increasing temporarily if the daily meat is put into the room at once. This capasity requirement is also subjected to a number of aproximations in the coolpack program. A somewhat different number can be as correct as the coolpack number.
    When I think about it if I have to size and select refrigeration plant for this. So working of the maximum capacity is probably the best option. For example if I size it at 3.6 kw and the temp does rises unexpected, the system will not be able to cope with the extra demand. If you catch my drift.

Similar Threads

  1. Maneurop MT51HK4A - Freezer Room
    By Hatchy in forum Trouble Shooting
    Replies: 35
    Last Post: 09-08-2010, 12:10 PM
  2. Blind Cold room specs help
    By frostedflake in forum Trouble Shooting
    Replies: 5
    Last Post: 13-03-2009, 01:49 AM
  3. Help with Condensation in Fitness Room
    By S_Line in forum Trouble Shooting
    Replies: 37
    Last Post: 04-03-2009, 12:52 AM
  4. Thawing Room (defrosting Room For Meat)
    By arunuae in forum Commercial
    Replies: 3
    Last Post: 09-02-2008, 09:24 AM
  5. Freezer Room Panels
    By Feeze in forum Technical Discussions
    Replies: 10
    Last Post: 22-04-2005, 05:58 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •