    Flooded Evaporator Too Warm



    We have an R507 flooded evaporator system that utilizes a Danfoss modulating suction valve to regulate the evaporator pressure/temperature. With the compressor running at 100% capacity we are seeing a 15 PSI pressure drop across the suction valve when the valve is wide open. Therefore when the evaporator pressure reaches 18 psig we have 3 psig at the compressor which results in a compressor low suction pressure kick-off.

    In the past we were able to achieve evaporator pressures of 8 psig without the compressor kicking off on low suction. We want this lower evaporator pressure/temperature to increase our cooling. Could this problem be the result of an over or under charged system? We always see the receiver tank partially full of liquid but at times also see liquid accumulate in the condenser?



  2. #2
    Join Date
    Feb 2008
    Location
    Norway
    Age
    57
    Posts
    446
    Rep Power
    17

    Re: Flooded Evaporator Too Warm

    Either the valve is horribly undersized or the valve is not fully open. What type of valve and what type of pilot valve? How do you know the valve is fully open? Is there an adjusting screw to manually force the valve fully open?

  3. #3
    Join Date
    Mar 2009
    Location
    USA
    Posts
    6
    Rep Power
    0

    Re: Flooded Evaporator Too Warm

    Yes, we forced the valve fully open with the adjustment screw. We suspected that their were valve related issues several weeks ago and replaced the valve with the exact same model as before.

  4. #4
    Join Date
    Feb 2008
    Location
    Norway
    Age
    57
    Posts
    446
    Rep Power
    17

    Re: Flooded Evaporator Too Warm

    Did you replace the pilot valve also?

  5. #5
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Flooded Evaporator Too Warm

    With a 15 psi pressure loss across the regulating valve it is either not open all of the way or too small as Mr. SteinarN mentioned. If the valve worked before and not now I suspect something is not allowing the valve to open properly.
    If all else fails, ask for help.


  6. #6
    Join Date
    Mar 2009
    Location
    USA
    Posts
    6
    Rep Power
    0

    Re: Flooded Evaporator Too Warm

    Thanks for the input from both of you. We did replace the valve with the same model as before and replaced the pilot as well. We bypassed the pilot and forced the valve open with the adjustment screw.

    I guess this is not a symptom that we would see with a correctly sized valve but an improperly charged system?

  7. #7
    roadienh3's Avatar
    roadienh3 Guest

    Re: Flooded Evaporator Too Warm

    Quote Originally Posted by larryd View Post
    We have an R507 flooded evaporator system that utilizes a Danfoss modulating suction valve to regulate the evaporator pressure/temperature. With the compressor running at 100% capacity we are seeing a 15 PSI pressure drop across the suction valve when the valve is wide open. Therefore when the evaporator pressure reaches 18 psig we have 3 psig at the compressor which results in a compressor low suction pressure kick-off.

    In the past we were able to achieve evaporator pressures of 8 psig without the compressor kicking off on low suction. We want this lower evaporator pressure/temperature to increase our cooling. Could this problem be the result of an over or under charged system? We always see the receiver tank partially full of liquid but at times also see liquid accumulate in the condenser?
    larryd,

    If you have measured 18 psig at the evaporator and 3 psig at the compressor, the 15 psig pressure drop you mention (far too much) is in the suction line. Perhaps there is a valve not open/ing all the way, or if the compressor has an inlet strainer, it may be partially plugged.

    roadie

  8. #8
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Flooded Evaporator Too Warm

    If a flooded evaporator is undercharged it may not have enough liquid to boil off to keep the suction pressure high enough, hence low suction pressure for undercharged.

    If the evaporator was overcharged you would have liquid running back the suction line (possibly) although the suciton pressure would be high enough because there is a sufficient volume of liquid in the evaporator.

    If the suction pressure is being recorded at 3 psig, where is this taken from (before or after the suction strainer, which is usually in the compressor or downstream from the suction service valve)?

    By any chance does this system have a hot gas bypass (feeding hot gas into the flooded evaporator)? And, what are the compressor motor amps now (compared to before)? And, is the compressor fully loaded (you said 100%, but I'm just asking)?
    If all else fails, ask for help.


  9. #9
    Join Date
    Mar 2009
    Location
    U.S.A.
    Posts
    320
    Rep Power
    20

    Re: Flooded Evaporator Too Warm

    The additional question added to US Iceman's is: Where is the Evap Pressure being taken? At the Regulator Access port or at the Evap itself or?

    If these are honest pressures and the regulator did not eat up 15-PSID in its past, the Part Number for the old and new reg and pilot should be re- checked. Is there a Suction Accumulator, Suction Filter and so on in between the points of pressure reading?

    How is the liquid level for the evaporator controlled? Has there been a drastic change in terms of the cooled fluid?

  10. #10
    Join Date
    Mar 2009
    Location
    USA
    Posts
    6
    Rep Power
    0

    Re: Flooded Evaporator Too Warm

    Sorry for the long delay, I have been on vacation. I suggested to the factory that the suction valve be replaced with a larger valve. The valve was replaced yesterday and they plan to test the system tomorrow or Wednesday. I will let you know if we see an improvement with the larger valve. Thanks again for your input.

  11. #11
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Flooded Evaporator Too Warm

    Is this a multiple evaporator system?

  12. #12
    Join Date
    Mar 2009
    Location
    USA
    Posts
    6
    Rep Power
    0

    Re: Flooded Evaporator Too Warm

    This is a single evaporator system.

    The good news is that the valve was replaced with a larger valve and much colder evaporator temperatures can now be achieved (-38 deg F). The Danfoss PM3-15 valve was replaced with a PM1-25.

    Thanks for all of your inputs.

Similar Threads

  1. John Lewis, fridge warm but freeze ok
    By netingit in forum Domestic
    Replies: 4
    Last Post: 21-08-2008, 01:23 AM
  2. Flooded & Pump Evaporators
    By MrReds in forum Fundamentals
    Replies: 3
    Last Post: 24-01-2007, 10:11 PM
  3. DX vs. flooded chiller
    By Nirmalya in forum Industrial
    Replies: 10
    Last Post: 16-08-2006, 07:09 PM
  4. HFCs for flooded systems?
    By garyb in forum Refrigerants
    Replies: 15
    Last Post: 21-04-2006, 10:02 PM
  5. Flooded Systems
    By bernard in forum Industrial
    Replies: 9
    Last Post: 21-07-2005, 01:44 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •