    carrier aircon units



    Can anyone help. We have a problem at work with 2 carrier split aircon units. They both run on hot or cold setting for approx 2 mins, then they shut down. We have had 3 different engineers out, and 2 said that it was the PCB, which was changed but did not rectify the problem. The other 1 said it was the thermo switch, which also was changed and also did not rectify the problem. Both units were well serviced, filters cleaned, gas checked etc...

    Any thought guys.
    Last edited by Brian_UK; 26-03-2009 at 11:09 PM. Reason: Post moved to correct forum.



  2. #2
    Join Date
    Jan 2009
    Location
    United Kingdom
    Age
    46
    Posts
    242
    Rep Power
    0

    Re: carrier aircon units

    Quote Originally Posted by jacko 63 View Post
    Can anyone help. We have a problem at work with 2 carrier split aircon units. They both run on hot or cold setting for approx 2 mins, then they shut down. We have had 3 different engineers out, and 2 said that it was the PCB, which was changed but did not rectify the problem. The other 1 said it was the thermo switch, which also was changed and also did not rectify the problem. Both units were well serviced, filters cleaned, gas checked etc...

    Any thought guys.
    You will need more info than this my friend. Refrigerant type, pressure and temperatures would help. Two simple questions: 1. Have they worked in the past ok? 2. If so..when did you notice the fault?
    Strange the two of them are under fault at the same time with the same problem. Is your set temps higher than your room temps in heating and vice versa in cooling?

  3. #3
    jacko 63's Avatar
    jacko 63 Guest

    Re: carrier aircon units

    they have worked fine till now.R22 is the gas and no the set temp is not higher than the room temp.These units are on seperate villas they both went down with this problem within 3 weeks of each other.

    thanks

    jacko 63

  4. #4
    jacko 63's Avatar
    jacko 63 Guest

    Re: carrier aircon units

    they have worked fine till now.R22 is the gas and no the set temp is not higher than the room temp.These units are on seperate villas they both went down with this problem within 3 weeks of each other.

    thanks

    jacko 63

  5. #5
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,450
    Rep Power
    41

    Re: carrier aircon units

    if units are shutting down so quickly it should be fairly handy to see why.

    Are you losing the compressor run command from the indoor?

    If not then the fault is on the outdoor, hp/lp switch or thermal overload, indoors are a different matter though.

    I think these old 22 units had a thermistor wired from the indoor to the outdoor, is this ok and is the inter connect ok and polarity correct??

    What kind of suction/discharge temps/pressures you getting, more info pleeeeeeease.

    al

  6. #6
    Join Date
    Jan 2009
    Location
    United Kingdom
    Age
    46
    Posts
    242
    Rep Power
    0

    Re: carrier aircon units

    When you say they shut down after 2 mins.....are they tripping the main fuse or do you receive a fault perhaps on the indoor unit. It could be a sequence of LED's flashing. I'm not familiar with carrier split systems fault code process but most split systems will have some sort of fault indication. Do the outdoor fans and compressors run?

Similar Threads

  1. Replies: 12
    Last Post: 27-03-2011, 04:12 AM
  2. Vrv
    By tgoonter in forum Air Conditioning
    Replies: 4
    Last Post: 11-01-2011, 06:25 AM
  3. New Building, New Units!!!
    By Fett in forum Air Conditioning
    Replies: 6
    Last Post: 19-11-2008, 03:43 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •