    Do I need a post-evaporator heat exchanger?



    I'm designing an R404a refrigeration system that has the evaporator approximately 18" below the compressor. In the past, I've always used a heat exchanger after the evaporator to ensure that no liquid enters the compressor. However, with the evaporator so far below the compressor, is there really a need for the heat exchanger? I would think that liquid entering would be very unlikely given these conditions.



  2. #2
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Do I need a post-evaporator heat exchanger?

    I don't see any significant advantage by installing heat exchanger but I would do more then usual to control oil return and liquid migration to the evaporator