    Danfoss Icad 900 actuator/motors



    Is anyone else having problems with the Danfoss ICAD 900. The trouble I'm having is that they are not closing or opening fully, sometimes. We are using them indoors, on flooded scape surface heat exchangers, as liquid feed and also as modulating suctions valves. The liquid feed is fully open or closed and might stay open for 5 or 6 days.
    Any ideas? Thanks, for any help.



  2. #2
    Join Date
    Mar 2005
    Location
    Belgium
    Age
    58
    Posts
    110
    Rep Power
    20

    Re: Danfoss Icad 900 actuator/motors

    Hi,
    here are some ideas:
    - check you're voltage supplied to the ICAD; not at the power supply but really at the ICAD terminals. Is it really 24Vdc ? Often I see the voltage supplied to the ICAd is too low (bad power supply, cables too long, wrong section, ...). And if this happens, sometimes there is not enough power to move the ICM.
    - Is there any ice build up between ICAD and ICM? Do you have a spindle heater installed?

  3. #3
    Join Date
    Mar 2009
    Location
    USA
    Age
    51
    Posts
    12
    Rep Power
    0

    Re: Danfoss Icad 900 actuator/motors

    We don't have any heaters. There is ice build up, we are having more trouble out of the ICADS that stay fully open, the ICADS that are modulating seem to work properly. My theory is that there is ice build up between the motor and the ICM when these valves don't move, and when it goes to close it slips and doesn't get back to fully closed. Also, some valves are failing with an A4 code in the MMI, which could be a power supply problem, correct? Thanks for your help.

  4. #4
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,758
    Rep Power
    46

    Re: Danfoss Icad 900 actuator/motors

    Hi rvmitch
    There are heater elements available for just your problem!
    Check out pages 7 + 58 for details in the manual I have posted.
    (see link below)
    Also check out pages 67 + 68 which are the alarm and parameter settings!

    A4 is "Low Fail Safe Supply"

    These valves are brilliant provided they are set up correctly.
    Did you log the parameter setting when you commissioned it?

    I definitely think you would benefit from the heaters mentioned and sorting out your fail safe supply.
    Good Luck Grizzly
    http://www.mediafire.com/?mjgmr5n5xcm
    Last edited by Grizzly; 26-03-2009 at 08:06 PM.

  5. #5
    Join Date
    Mar 2009
    Location
    USA
    Age
    51
    Posts
    12
    Rep Power
    0

    Re: Danfoss Icad 900 actuator/motors

    Thanks grizzly.
    I have 3 heaters I'm going to install when we have some down time. I talked them into 3 to test the idea, we have about 80 Icads so they were a little reluctant to spend $20,000 on these heaters if they don't work.

  6. #6
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,758
    Rep Power
    46

    Re: Danfoss Icad 900 actuator/motors

    Quote Originally Posted by rvmitch9927 View Post
    Thanks grizzly.
    I have 3 heaters I'm going to install when we have some down time. I talked them into 3 to test the idea, we have about 80 Icads so they were a little reluctant to spend $20,000 on these heaters if they don't work.
    Wow!
    What a lot of valves.
    That's good sensible approach to the problem.
    Incidentally do you have fail safe supplies fitted?
    As they are an optional extra.
    Grizly

  7. #7
    Join Date
    Mar 2009
    Location
    USA
    Age
    51
    Posts
    12
    Rep Power
    0

    Re: Danfoss Icad 900 actuator/motors

    No we don't have the fail safe installed. You are talking about the back up battery, right?

  8. #8
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,758
    Rep Power
    46

    Re: Danfoss Icad 900 actuator/motors

    Quote Originally Posted by rvmitch9927 View Post
    No we don't have the fail safe installed. You are talking about the back up battery, right?
    Yep!
    Grizzly

Similar Threads

  1. Too dependent on Danfoss Valves
    By kelvin_27_84 in forum Industrial
    Replies: 8
    Last Post: 24-01-2009, 09:33 PM
  2. York ycaj Danfoss EKS65 phtq info
    By tomireland in forum Trouble Shooting
    Replies: 13
    Last Post: 22-12-2008, 07:47 PM
  3. Problems Danfoss Safetyvalve
    By Bart Nabbe in forum NH3
    Replies: 7
    Last Post: 26-06-2008, 09:05 PM
  4. DANFOSS / DEAN and WOOD
    By Grizzly in forum Legal-Business-Marketing
    Replies: 1
    Last Post: 08-12-2007, 08:29 PM
  5. Danfoss Compressors
    By iceman007 in forum Fundamentals
    Replies: 0
    Last Post: 28-07-2006, 06:32 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •