    Charging liquid into suction line



    Hi

    I learnt and also advise my students never charge liquid into suction line.

    However I found a manual which states to charge R407 into the suction line in liquid form.

    Please help me understand how the compressor will deal with liquid refrigerant in the suction line

    I download the manual and uploaded it to my site

    acrisoft.bizland.com + mms_i.pdf

    The manual belongs to:
    McQuay International


    Moises



  2. #2
    Join Date
    Nov 2005
    Location
    wales
    Posts
    66
    Rep Power
    20

    Re: Charging liquid into suction line

    R407C must be charged in liquid state as it's a blend. As for charging directly in to suction I would say it all depends on how much you need to charge in and how close to the compressor you are. If you charge through a shreader connection allowing the gas to flash off slowly you should be ok. Yellow jacket also sell an adaptor for your bottle connector allowing you to safley charge liquid to sucton.

  3. #3
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: Charging liquid into suction line

    Never is a very big word.

    Me for example, I usually charge liquid into suction line but mostly before the liquid separator.

    Many new blends can only be charged as liquid.

    If you control the liquid amount and watch carefully that the oil in the compressor does not have too much liquid refrigerant, no problems and a lot of time saved.

    This of course require experience and knowledge of the system you charge.

  4. #4
    Join Date
    Dec 2004
    Location
    manchester
    Posts
    97
    Rep Power
    20

    Re: Charging liquid into suction line

    Quote Originally Posted by chemi-cool View Post
    Never is a very big word.

    Me for example, I usually charge liquid into suction line but mostly before the liquid separator.

    Many new blends can only be charged as liquid.

    If you control the liquid amount and watch carefully that the oil in the compressor does not have too much liquid refrigerant, no problems and a lot of time saved.

    This of course require experience and knowledge of the system you charge.
    Is this another term for suction accumilator?

  5. #5
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: Charging liquid into suction line

    Yes. Thats the one.

  6. #6
    Join Date
    Aug 2009
    Location
    Turhona.libya
    Posts
    79
    Rep Power
    15

    Re: Charging liquid into suction line

    Charging the new blends in a liquid phase does not mean charging it via the compressor's suction port . If we know the amount that a system required,we could use charging cylinder. We could use the easy charge adaptor.never charge the refrigerant in the liquid phase through the suction port means never. And compressor manufacturers recommendations always advice us not to charge the refrigerant through suction port incase of oil migrant and also valve damage. remember that the compressor is a machine to compress only vapour .

  7. #7
    Join Date
    Feb 2008
    Location
    adelaide sth.oz
    Posts
    1,015
    Rep Power
    19

    Re: Charging liquid into suction line

    charge using a cappillary line if your overly concerned
    mmm to beer or not to beer...........lets drink breakfast

  8. #8
    Join Date
    Jul 2010
    Location
    Santarem
    Posts
    5
    Rep Power
    0

    Re: Charging liquid into suction line

    Hi there.
    I need to charge my A/C that uses R407C but I am confused about protocol to follow.
    I ave read that the R 407C must be charge in liquid state, that seem obvious to me but is a problem, I think, to get the ***** inside by the service port.
    I am wondering if it is possible to use a "transfer bottle".
    The point is: Charge a small cilinder with the exact amount of R 407 we need, ant then charge the A/C via service port, and in vapor state.
    I don't know much about refrigeration, so I ask for help in this situation. I really need to charge that machine.

    Any help will be appreciated.

  9. #9
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: Charging liquid into suction line

    Quote Originally Posted by tapadas View Post
    Hi there.
    I need to charge my A/C that uses R407C but I am confused about protocol to follow.
    I ave read that the R 407C must be charge in liquid state, that seem obvious to me but is a problem, I think, to get the ***** inside by the service port.
    I am wondering if it is possible to use a "transfer bottle".
    The point is: Charge a small cilinder with the exact amount of R 407 we need, ant then charge the A/C via service port, and in vapor state.
    I don't know much about refrigeration, so I ask for help in this situation. I really need to charge that machine.

    Any help will be appreciated.
    Charge in liquid form, it is quite simple.

    Connect the bottle to the system via your manifold set as usual.

    Open the bottle valve, if it has a dip-tube fine if not then invert the bottle so that liquid will come out.

    Now crack open the valve on your manifold set so that the liquid is expanded through the valve into a vapour mix before entering the system.

    Liquid has come out of the bottle and that is what must happen.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  10. #10
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    52
    Posts
    2,554
    Rep Power
    24

    Re: Charging liquid into suction line

    chemi-cool has got it right.
    After all, you wouldn't be able to charge a system in the liquid line this time of the year.

  11. #11
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34

    Re: Charging liquid into suction line

    You can do it easily with a recovery station which we always we do when we recovered gs for a repair.
    Station is already on-site with the right gas on the inside of the unit, no need to vacuum it again.
    And we don't have to calculate the amount of gas, all what was recovered goes back in it again.
    Handy when working on VRV's or VRF's which need a correct amount of gas...they say
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  12. #12
    Join Date
    Jul 2009
    Location
    dublin
    Age
    41
    Posts
    47
    Rep Power
    0

    Re: Charging liquid into suction line

    Dont scrolls allow for easier charging of liquid through the suction? I think they handle it better because it wont try to compress the liquid, there is a valve that lifts and allows the liquid to pass through with compression occurring........i think

  13. #13
    Join Date
    Jul 2010
    Location
    Santarem
    Posts
    5
    Rep Power
    0

    Re: Charging liquid into suction line

    HTML Code:
    Charge in liquid form, it is quite simple.
    
    Connect the bottle to the system via your manifold set as usual. 
    
    Open the bottle valve, if it has a dip-tube fine if not then invert the  bottle so that liquid will come out. 
    
    Now crack open the valve on your manifold set so that the liquid is  expanded through the valve into a vapour mix before entering the system. 
    
    Liquid has come out of the bottle and that is what must happen.
    Thanks Brian!

    The situation is now clear for me.
    When the liquid reaches the valve it passes to vapour phase due the low pressure on the other side of the line.
    I suppose that happens because the compressor create a very low pressure on the service port vaporizing the ***** as son as it pass through the valve.
    I have another question, sorry for the inconvenience, its possible the manifold freeze due the ***** expansion before entering in the suction port?

  14. #14
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: Charging liquid into suction line

    Quote Originally Posted by tapadas View Post
    I have another question, sorry for the inconvenience, its possible the manifold freeze due the ***** expansion before entering in the suction port?
    Yes, you can get frost on the manifold but remember that in most cases you are also using the valve core in the access port as another expansion device.

    Do it sensibly and you will soon get a 'feel' for how much to set the manifold valve at.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  15. #15
    Join Date
    Jul 2010
    Location
    Santarem
    Posts
    5
    Rep Power
    0

    Re: Charging liquid into suction line

    Thanks Brian.
    Now, I feel some confidence to do the job in next weekend.

  16. #16
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    52
    Posts
    2,554
    Rep Power
    24

    Re: Charging liquid into suction line

    Quote Originally Posted by Collie View Post
    Dont scrolls allow for easier charging of liquid through the suction? I think they handle it better because it wont try to compress the liquid, there is a valve that lifts and allows the liquid to pass through with compression occurring........i think

    Well, I've seen scroll compressors crushed because of liquid slugging anyway, despite being more tolerant.

  17. #17
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34

    Re: Charging liquid into suction line

    I have a case for the Court where 8 Maneurop/Danfoss scrolls broke within 2 years on a Carrier chiller.
    I have pictures of the inside, the scroll is completely gone.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  18. #18
    Join Date
    Jul 2008
    Location
    london
    Posts
    102
    Rep Power
    16

    Re: Charging liquid into suction line

    Can't you charge the liquid threw a vac? That's what I do mostly. if you can't get it all in from vac then some equipment allows you to put it into a pump down mode to charge refrigerant. If not slowly metering it threw gauges into system can be done. Like previously said be carefully as comp shouldn't recieve liquid....

  19. #19
    Join Date
    Jul 2010
    Location
    Santarem
    Posts
    5
    Rep Power
    0

    Re: Charging liquid into suction line

    Thank´s guys.

    Last weekend I charged my machine with 730g of R 407C.
    It was a piece of cake. I used a "transfer bottle" made of a spent oxygen bottle with a small valve fit on.
    I put the bottle in a bucket of frozen salt water on top of a kitchen scale and charged it this way connected to the main bottle that was up side down, I made vacuum in the line and seal the vac pump line. After that I opened slowly the main tank valve and it took me about two minutes to get the 730g in the small bottle, an easy job to do.

  20. #20
    zack217's Avatar
    zack217 Guest

    Re: Charging liquid into suction line

    It is possible to charge liquid into collector/receiver after the condenser instead of to suction line of compressor. However, the system maybe does not have collector/receiver.

  21. #21
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    52
    Posts
    2,554
    Rep Power
    24

    Re: Charging liquid into suction line

    Yes, it is not only possible, but recommended, if you have one installed.

  22. #22
    Join Date
    Aug 2009
    Location
    Torokszentmiklos
    Age
    51
    Posts
    23
    Rep Power
    0

    Re: Charging liquid into suction line

    Quote Originally Posted by Acrisoft View Post
    Hi

    I learnt and also advise my students never charge liquid into suction line.

    However I found a manual which states to charge R407 into the suction line in liquid form.

    Please help me understand how the compressor will deal with liquid refrigerant in the suction line

    I download the manual and uploaded it to my site

    acrisoft.bizland.com + mms_i.pdf

    The manual belongs to:
    McQuay International


    Moises
    I think
    use a safety charge adapter from yellov jacket
    or use a capillary or use a transfer bottle, or charge liquid slowly and if you hear a furry noise then stop a bit.

    No hazard without risk !

Similar Threads

  1. Superheat and Subcooling
    By Chunk in forum Fundamentals
    Replies: 42
    Last Post: 15-01-2011, 02:24 AM
  2. Liquid charging through the suction side
    By deu58 in forum Fundamentals
    Replies: 13
    Last Post: 02-07-2010, 05:23 AM
  3. Charging liquid through suction line?
    By SloFuse in forum Trouble Shooting
    Replies: 15
    Last Post: 20-06-2010, 09:26 PM
  4. Benji
    By benji in forum Trouble Shooting
    Replies: 29
    Last Post: 30-01-2008, 02:25 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •