    Sanyo SPW E04 Fault



    Hi

    I have a Sanyo split system controller has E04 fault
    (communications fault outdoor unit).
    When I checked found main PCB not powered up although power supply ok to condenser.
    Apparantly another company has already tried changing main pcb and power pcb with no effect.
    There is a small compressor pcb with appears to have some damage to it. When I dissconnect the compressor from it the main pcb comes back to life
    Compressor meters ok - although it may be seized.

    Just wondered if anyone has similar experiance and does anyone have a technical manual for this unit

    Sanyo SPWCR484GVH56

    Thanks



  2. #2
    Join Date
    Jul 2005
    Location
    Ireland
    Age
    57
    Posts
    164
    Rep Power
    19

    Re: Sanyo SPW E04 Fault

    Hi Carlos,

    The E04 is as you say a communication breakdown between the indoor unit and the outdoor unit.

    If as you say the main PCB and Power Filter PCB has been changed then it is safe to assume these are OK.(although assumption is the mother of all **** ups)

    So if you disconnect the HIC PCB does communication stabilise between the indoor unit and outdoor unit??

    IE Does E04 vanish?? If not you may still have a problem with your Power filter PCB the voltage for communication is generated on this PCB


    The compressor PCB is called a HIC pcb it's basically a transistor PCB. This can be tested as follows.

    1. Disconnect the HIC + and HIC- wires and ensure <330 volts DC is present.
    2. If Yes great switch off power. If not, not great maybe your Bridge Diode is faulty.
    3. If Yes and power is switched off ensure the
    Capacitors on the Power PCB have discharged Then disconnect all wiring from the HIC PCB and check the resistance across the differant terminals as follows

    HIC+ to HIC - 200 Kohms or more
    HIC+ to U 300 Kohms or more
    HIC+ to V 300 Kohms or more
    HIC+ to W 300 Kohms or more
    HIC- to U 200 Kohms or more
    HIC- to V 200 Kohms or more
    HIC -to W 200 Kohms or more

    Outside the above the HIC PCB is faulty if this is faulty it is likely the compressor has caused this damage.



    As you have said the compressor may be sized if so. I would recommend changing the HIC PCB and the compressor.

    Sorry about doc can't upload because of site limitations drop me a pvt message with a mail address and I'll send you a manual.

    T
    Last edited by techguy; 04-10-2010 at 03:46 PM.

Similar Threads

  1. Older Sanyo Cassette fault codes
    By climacool in forum Air Conditioning
    Replies: 4
    Last Post: 16-02-2009, 05:23 PM
  2. Sanyo Text Back Fault Code Service
    By techguy in forum Air Conditioning
    Replies: 1
    Last Post: 04-02-2009, 06:57 PM
  3. Sanyo fault codes
    By Slim R410a in forum Air Conditioning
    Replies: 3
    Last Post: 03-11-2008, 08:02 PM
  4. fault on a sanyo unit
    By marc5180 in forum Air Conditioning
    Replies: 7
    Last Post: 18-08-2007, 11:04 PM
  5. MHI, Sanyo & Fuijitsu Complete Fault Codes
    By aeb200 in forum Air Conditioning
    Replies: 1
    Last Post: 16-11-2005, 01:11 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •