    Refrigerant load to elect load



    Hi All,

    How to convert refrigerant load to elect load.

    Say eg: from 2,400,000btu/hr to kw.



    Thanks & Regards



  2. #2
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    64
    Posts
    2,212
    Rep Power
    20

    Re: Refrigerant load to elect load

    Have you read up on the term:

    COP = coefficient of performance ?

  3. #3
    Join Date
    Mar 2007
    Location
    singapore
    Posts
    19
    Rep Power
    0

    Re: Refrigerant load to elect load

    no have not read that.
    just want to find out the power consumsion.

  4. #4
    Join Date
    May 2008
    Location
    Belgium
    Age
    66
    Posts
    802
    Rep Power
    16

    Re: Refrigerant load to elect load

    Sparo, your laizy, google on to Wikipedia and type C.O.P ,coifficient of performance, and you get all the info you want.

    laizy bom, Ice

  5. #5
    Join Date
    Jul 2008
    Location
    London
    Posts
    848
    Rep Power
    17

    Re: Refrigerant load to elect load

    2.4m BTU -that's a fair old tonnage!

    (Just to confuse things further ;-)

  6. #6
    Join Date
    May 2009
    Location
    Pakistan
    Age
    42
    Posts
    5
    Rep Power
    0

    Re: Refrigerant load to elect load

    Quote Originally Posted by sparo View Post
    Hi All,

    How to convert refrigerant load to elect load.

    Say eg: from 2,400,000btu/hr to kw.



    Thanks & Regards
    To convert 2400000 btu/hr to kw procedure is

    1 btu/hr is equal to 2.928 kw so u convert easily .ok buddy.

  7. #7
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Refrigerant load to elect load

    ^ but that is not the electrical consumption required which was his question.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  8. #8
    Join Date
    Aug 2007
    Location
    UK
    Age
    42
    Posts
    135
    Rep Power
    17

    Re: Refrigerant load to elect load

    Just commissioning 2 chillers in Minnesota at 5.5M BTU/hr each. had to convert everything to kW ref load to BTU and C to F time the americans joined the rest of the world and used SI i say.

  9. #9
    Join Date
    May 2006
    Location
    India
    Age
    74
    Posts
    399
    Rep Power
    18

    Re: Refrigerant load to elect load

    240,0000 btu/hr = 200 TR

    2OO TR DIVIDED BY 0.2845 = 702.98 KW

  10. #10
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Refrigerant load to elect load

    Quote Originally Posted by sparo View Post
    Hi All,

    How to convert refrigerant load to elect load.

    Say eg: from 2,400,000btu/hr to kw.



    Thanks & Regards
    Quote Originally Posted by D.D.KORANNE View Post
    240,0000 btu/hr = 200 TR

    2OO TR DIVIDED BY 0.2845 = 702.98 KW
    Quote Originally Posted by Brian_UK View Post
    ^ but that is not the electrical consumption required which was his question.
    .........................................
    Last edited by nike123; 19-05-2009 at 01:57 PM.

  11. #11
    Join Date
    Aug 2008
    Location
    Baltics
    Age
    62
    Posts
    786
    Rep Power
    16

    Re: Refrigerant load to elect load

    I use such, however, a very, very rough conversion: 1000 W electrical = 3000 W heat = 9000 Btu (also "heat", of course), simply, a mnemonic: 1-3-9, and vice versa.

  12. #12
    Join Date
    Aug 2008
    Location
    Baltics
    Age
    62
    Posts
    786
    Rep Power
    16

    Re: Refrigerant load to elect load

    This concerning the choice of a comp for an AC. I believe, I have not confused the numbers unforgivably.

Similar Threads

  1. Superheat and Subcooling
    By Chunk in forum Fundamentals
    Replies: 42
    Last Post: 15-01-2011, 01:24 AM
  2. Leak Testing?
    By Thana in forum Trouble Shooting
    Replies: 36
    Last Post: 31-08-2010, 02:57 PM
  3. MHI FDCA400HKXRE4 Tech Info Please
    By L.JT in forum Trouble Shooting
    Replies: 5
    Last Post: 23-08-2008, 11:00 PM
  4. Compressor loading, cooling, and range of operation.
    By Air duster in forum Fundamentals
    Replies: 10
    Last Post: 02-04-2008, 08:39 AM
  5. fun quiz
    By Brian23 in forum New to RE
    Replies: 6
    Last Post: 02-10-2007, 10:18 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •