    Daikin roundflow noisey



    Anyone had experience of Daikin roundflow cassettes on a VRVIII 3 pipe? The roundflows always seem a bit "hissy" (refrigerant flow noise through EEV) but I have 2 that are even worse, a real loud gargling/slurping type sound...weird!
    Both happen to be sharing a BS box with another roundlow cassette, that is not so noisy. The pipework, refnets, and BS boxes have been checked (EEV heads fully on & "clicked in place") and both fan coil EEV's have been "refrenced", this has reduced the noise a bit, but I am half expecting complaints to follow, along the lines of "by A/C sounds like a cistern filling/draining"!!

    Any feedback much appreciated.

    LAF100


    "I'm anaspeptic, frasmotic, even compunctuous to have caused you such pericombobulation."

  2. #2
    Join Date
    Feb 2009
    Location
    england
    Posts
    22
    Rep Power
    0

    Re: Daikin roundflow noisey

    A service engineer i know had a similar noise from some mitsi vrfs in Bath and he was told to change the refrigerant gas by Mitsi technical.Once he did this the noise was cured. If you speak to Daikin the first thing that they will say will be do you know if the charge is correct. Guarenteed

  3. #3
    Join Date
    Jan 2007
    Location
    UK
    Age
    53
    Posts
    82
    Rep Power
    18

    Re: Daikin roundflow noisey

    I would usually do the same thing, but the noise was found during commissining.... by a "daikin" engineer!! Charge was calculated & added by them, fan coil performance is fine. He was baffled as well.
    "I'm anaspeptic, frasmotic, even compunctuous to have caused you such pericombobulation."

  4. #4
    Join Date
    Mar 2009
    Location
    uk
    Age
    61
    Posts
    5
    Rep Power
    0

    Re: Daikin roundflow noisey

    I have heard of this happening alot more than it should from several people, especially when the cassettes are on VRVs.

    Will the manufacturer (Daikin) own up and say there is a problem?

    Or will they just wait until people start to install other manufacturers kit instead before they rectify it?

Similar Threads

  1. Daikin not working... many problems
    By stankovicv in forum Air Conditioning
    Replies: 26
    Last Post: 11-12-2010, 09:01 AM
  2. Daikin, Why do we bother?
    By gwilliamson in forum Air Conditioning
    Replies: 21
    Last Post: 02-02-2010, 09:38 AM
  3. Fixing Daikin A3 Error
    By Stuffy in forum Air Conditioning
    Replies: 3
    Last Post: 27-03-2009, 06:02 AM
  4. Getting a price from Daikin....
    By monkey spanners in forum Chit Chat & Service Stories
    Replies: 4
    Last Post: 17-08-2008, 09:46 PM
  5. fault on a daikin Roundflow
    By marc5180 in forum Air Conditioning
    Replies: 65
    Last Post: 12-08-2008, 10:15 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •