    Question Freezer Flatlining



    I got a ColdTech/Minus Forty upright single door freezer which is giving me some problem.

    What i mean by flatlining is that it never reaches its designed temperature which is set by thermostat.

    Set point is set for -20 F But it only reaches to about -9 and keeps cycling.

    Its charged with 404
    Temperature probe is properly installed
    Control was replaced with new digital one but no luck.

    What could it possibly be?



  2. #2
    Join Date
    Feb 2007
    Location
    newcastle but now carlisle
    Age
    53
    Posts
    195
    Rep Power
    18

    Re: Freezer Flatlining

    is r404 on the cascade side of it. just thats a bit cold for r404. need mo info ie. is there a subcooler ? wat is the second stage doing ? (if it has 1 )pressures stuff like that

  3. #3
    Join Date
    Jun 2007
    Location
    Canada
    Age
    42
    Posts
    21
    Rep Power
    0

    Re: Freezer Flatlining

    This is not a cascade system.. Its a upright single glass door merchandiser.
    Its a closed system.

  4. #4
    Join Date
    Jan 2009
    Location
    Queensland
    Age
    65
    Posts
    113
    Rep Power
    16

    Re: Freezer Flatlining

    You say:
    Set point is set for -20 F But it only reaches to about -9 and keeps cycling.
    So what is it cycling on?
    if not the thermostat, is it cycling on an LP control?

  5. #5
    Join Date
    Jun 2007
    Location
    Canada
    Age
    42
    Posts
    21
    Rep Power
    0

    Re: Freezer Flatlining

    This unit has a digital controller that can be adjusted. I changed the controller and still same thing.

    I finally solved the mystery and it was low refrigerant that was causing it to have low SC and High SH

  6. #6
    Join Date
    Feb 2007
    Location
    newcastle but now carlisle
    Age
    53
    Posts
    195
    Rep Power
    18

    Re: Freezer Flatlining

    sultan

    not much of a mystery after all . if it was just short of gas .
    Last edited by tony--1; 21-03-2009 at 06:41 PM.

  7. #7
    Join Date
    Jan 2009
    Location
    Queensland
    Age
    65
    Posts
    113
    Rep Power
    16

    Re: Freezer Flatlining

    So where was the leak?
    I trust you found and fixed it?

Similar Threads

  1. ice cream truck freezer
    By GaryC in forum Transport
    Replies: 7
    Last Post: 06-12-2008, 02:19 AM
  2. Hotpoint FFA71 Freezer High Temp Light / Fridge is Freezing
    By sumnerpa in forum Trouble Shooting
    Replies: 1
    Last Post: 19-08-2008, 03:16 PM
  3. Freezer compressor running 20 Hours/day
    By rickcw in forum Domestic
    Replies: 12
    Last Post: 08-03-2008, 11:50 PM
  4. Need help quick with walk-in freezer issues!
    By hysiderafter in forum Commercial
    Replies: 5
    Last Post: 12-12-2007, 12:57 AM
  5. Trolley freezer & blast freezer
    By smpsmp45 in forum NH3
    Replies: 0
    Last Post: 25-08-2007, 07:29 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •