Thread: heat calc
-
20-03-2009, 07:24 AM #1
heat calc
what value of watts metre 2 should i use for air conditioining a electronic gaming machine room (pokey machines)
-
22-03-2009, 07:34 PM #2
Re: heat calc
how mutch heatloss or watt consumption do the have? how many people is there in the room? howmany lights,spots ect..
its the same basic calc like for a office.....
Ice
-
07-04-2009, 12:42 PM #3
Re: heat calc
how to calculate the heat load for Ice cream storage room . we want the capacity of the cold room is 25,000 liters ice cream storage. input temperature of the ice cream is -4 deg C and dispatch ice cream temperature is -20 deg c . Door opening 50-120 times /day , 4-7 worker work in the room.
-
07-04-2009, 12:55 PM #4
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: heat calc
What are room dimensions (W-L-H)?
What are temperatures at other side of room panels?
What is infiltration air max temperature?
Does the floor insulated?
What are material and thickness of room walls?
Describe room placement?
What is pull down time?
Any forklifts?
50-120 openings is lot. You should consider air curtain.
P.S. Next time "please" instead of "I want" will be nicer.Last edited by nike123; 07-04-2009 at 12:58 PM.
-
07-04-2009, 05:46 PM #5
-
13-04-2009, 06:25 PM #6
Re: heat calc
To do it right, you will need the heat dissapation of each machine. There are several possiblilities: You can only get the motor watts and amps. Since the machine does not operate continuously, you would need to find out from the owner about what percentage of each hour a typical machine is in use. If that is given the symbol u for usage factor, then the total heat dissapated per machine would be Q=V*I*u. ; Often, the machine manufacturer can give you the operational and standby heat dissapation, which would be better than using the input.
Similar Threads
-
Capacity control
By sparrow in forum TrainingReplies: 44Last Post: 18-01-2010, 07:49 PM -
Some information on the aplication of suction gas/liquid line heat exchangers
By SteinarN in forum FundamentalsReplies: 5Last Post: 14-09-2009, 07:33 AM -
Pool heat pump water side diagram
By nike123 in forum Heat PumpsReplies: 23Last Post: 22-03-2009, 07:42 PM -
frostles heat pump
By Lc_shi in forum New TechnologiesReplies: 27Last Post: 31-03-2008, 07:53 AM -
Heat Transfer calc on Falling Film Evap type on Tube Icemaker
By llewelyn in forum FundamentalsReplies: 4Last Post: 11-05-2007, 02:15 AM