    Pool heat pump water side diagram



    Hi guys! I have customer who want to connect his home heat pump to heat pool during mild and cool weather.
    It has 45 kW heat pump with desuperheater for heating domestic hot water, and I proposed to him that he could use that heat exchanger for that purpose.
    I don't have any experience in pool installations so I need diagram of ordinary pool instalation with heat exchanger for additional heating from heat pump since pool have his own heater by electricity.

    I thinking to connect heat pump heat exchanger before pool electrical heater so that pool automatic could remain untouched and only regulation for desuperheater circuit should be one 3-way valve for bypassing the heat exchanger when temperature in pool has reached.
    Does anyone have any schematic diagram of such existing system and how control of this combination should be done without touching pool electronics.
    It should work on desuperheater only, when heat is available from heat pump and at electrical heater, when there is no heat availiable from heat pump.



  2. #2
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Pool heat pump water side diagram

    Years ago I have made a heater, gas operated with PHE and pumps. If you are interested, I can draw you something and email it to you.

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Pool heat pump water side diagram

    One thing to be aware of Nike.

    Will the pool chemicals, chlorine etc., affect the metals of the desuperheater?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Pool heat pump water side diagram

    Quote Originally Posted by Brian_UK View Post
    One thing to be aware of Nike.

    Will the pool chemicals, chlorine etc., affect the metals of the desuperheater?
    It is not direct heat transfer. It first heat water in closed loop, and at pool side is going to be second heat exchanger for pool water heating of proper material (titane, I think). It is going to be supplied and installed by original pool equipment installations company.
    Last edited by nike123; 20-03-2009 at 06:21 AM.

  5. #5
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Pool heat pump water side diagram

    Quote Originally Posted by chemi-cool View Post
    Years ago I have made a heater, gas operated with PHE and pumps. If you are interested, I can draw you something and email it to you.

    That would be nice, thanks!

    What is your opinion about if I should put heat exchanger (hat pump one) before swimming pool original electrical heater or after him, regarding of control problem?

  6. #6
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Pool heat pump water side diagram

    This is pool electrical heater (i think 18kW)


    Anyone recognize manufacturer or model? It is blured image, something like Titane or Titanic or Titank.

    This is 45kW Galletti heat pump for cooling and heating house, and it has desuperheater for heating domestic hot water, and we already made before branch for swimming pool heat exchanger.



  7. #7
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Pool heat pump water side diagram

    Hi Nike,

    Please leave me your email in my PM and I prepare it for you or you prefer it here. Whatever.

  8. #8
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Pool heat pump water side diagram

    Quote Originally Posted by chemi-cool View Post
    Hi Nike,

    Please leave me your email in my PM and I prepare it for you or you prefer it here. Whatever.
    E-mail adress sent!

  9. #9
    Join Date
    Aug 2008
    Location
    ENGLAND
    Age
    54
    Posts
    27
    Rep Power
    0

    Re: Pool heat pump water side diagram

    Hi,
    On a standard pool installation you will always install the heat pump before any other form of heating, so you will need to put your heat exchanger before the electric heater.
    Do not recognise that electric heater, not something i have seen in this country.

  10. #10
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Pool heat pump water side diagram

    I have noticed that the pipes entering and leaving the electric heater are not insulated. Thats odd.

    Standard heat pump is a slow heater and always have a large reservoir.

    How much water in the pool? [C\M]?
    Is the pool indoors?
    What water temp do you want to achieve?

  11. #11
    Join Date
    Aug 2008
    Location
    ENGLAND
    Age
    54
    Posts
    27
    Rep Power
    0

    Re: Pool heat pump water side diagram

    No swimming pool pipework is insulated on an indoor or outdoor pool.

  12. #12
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Pool heat pump water side diagram

    No swimming pool pipework is insulated on an indoor or outdoor pool.
    Why?

    It doe's not make any sense.

  13. #13
    Join Date
    Nov 2006
    Location
    UK
    Age
    50
    Posts
    708
    Rep Power
    23

    Re: Pool heat pump water side diagram

    Quote Originally Posted by chemi-cool View Post
    Why?

    It doe's not make any sense.
    I have never worked on pools at all before but I have seen many unisulated instalations and always wondered why pipe work was never insulated seems strange to me

  14. #14
    Join Date
    Aug 2008
    Location
    ENGLAND
    Age
    54
    Posts
    27
    Rep Power
    0

    Re: Pool heat pump water side diagram

    In a pool pipework system there are so many places where heat loss can occur. ie, sand filters which are uninsulated and can be anything up to 8 feet square, so insulating the pipework would be a bit pointless and as you are only trying to achieve temperatures of between 27 and 30 degrees c, the ambient temperature is normally not much lower than this in a majority of pool plant rooms. Most of the pool pipework is underground, often with only about 4-5 meters of pipe above ground on your average domestic pool.

  15. #15
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Pool heat pump water side diagram

    Just for a civilized argue,

    Insulation is a matter expenses, everything can be well insulated, pipes, filters, valves....

    you generally heat pools in the winter [which is about 8 months a year in the UK]

    Ground temp 1 meter deep will not be over 10°C......

    And so on. To my humble opinion it is bad practice!

  16. #16
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Pool heat pump water side diagram

    Sorry guys, I was been away from my computer till now.

  17. #17
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Pool heat pump water side diagram

    Quote Originally Posted by chemi-cool View Post
    I have noticed that the pipes entering and leaving the electric heater are not insulated. Thats odd.

    Standard heat pump is a slow heater and always have a large reservoir.

    How much water in the pool? [C\M]?
    Is the pool indoors?
    What water temp do you want to achieve?

    As CHIZEL010 already said, it is common practice that pool pipes are not insulated. Maybe that is because they are plastic with thick wall. Low heat loss.

    Pool is about 8x10x2m (160^3)
    Pool is outdoor in mild Mediterranean climate!
    25°C in cold days is target temperature. Pool is outdoors.
    It is goal to use as much is possible heat from /air conditioner/heat pump, but only when air conditioner works for heating/cooling house and rest of heat should be added with electrical heater.

    I think that electrical heater is of 20 kw power.
    Last edited by nike123; 21-03-2009 at 05:55 PM.

  18. #18
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Pool heat pump water side diagram

    This is diagram what is done and what is planed (in red).

  19. #19
    Join Date
    Feb 2008
    Location
    Norway
    Age
    57
    Posts
    446
    Rep Power
    17

    Re: Pool heat pump water side diagram

    The function of the 3-way valves is not clear from the drawing, what side is always open?

    Have you considered how much heat is really available? What does the refrigeration system do normally? Heating or cooling something?

  20. #20
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Pool heat pump water side diagram

    Quote Originally Posted by SteinarN View Post
    The function of the 3-way valves is not clear from the drawing, what side is always open?

    Have you considered how much heat is really available? What does the refrigeration system do normally? Heating or cooling something?
    That depend on house heat loss and gain in different weather conditions, so main goal is use rejected heat in cooling season and use of cheaper heat in heating season. No calculation is done but maximum what desuperheater could produce is about 12-15kW when both compressor are running (system have got 2 refrigerant circuits)


  21. #21
    Join Date
    Feb 2008
    Location
    Norway
    Age
    57
    Posts
    446
    Rep Power
    17

    Re: Pool heat pump water side diagram

    Is it necessary to stop the circulation to the hot water tanks any time? Can this water be to hot? If not then I propose to do like this:

    When the hot water is satisfied the valve is alowed to switch to swiming pool position if heat is required. I dont know how to make the signal for the swimming pool heat required. Is it possible to take a signal from the swimming pool heat regulator?
    Attached Images Attached Images
    Last edited by SteinarN; 22-03-2009 at 05:15 PM.

  22. #22
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Pool heat pump water side diagram

    Quote Originally Posted by SteinarN View Post
    Is it necessary to stop the circulation to the hot water tanks any time? Can this water be to hot? If not then I propose to do like this:

    When the hot water is satisfied the valve is alowed to switch to swiming pool position if heat is required. I dont know how to make the signal for the swimming pool heat required. Is it possible to take a signal from the swimming pool heat regulator?

    It is alredy installed like that and it is not option to remove it. Main reason for this setup is here:
    Last edited by nike123; 22-03-2009 at 05:35 PM.

  23. #23
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Pool heat pump water side diagram

    Duplicate post.
    Last edited by nike123; 22-03-2009 at 05:35 PM.

  24. #24
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Pool heat pump water side diagram

    I found something useful in Alfa Laval documentation. Any comment?


Similar Threads

  1. cold river water
    By eftimios in forum Fundamentals
    Replies: 8
    Last Post: 09-11-2008, 06:37 PM
  2. Home designed and built heat pump!
    By The MG Pony in forum Heat Pumps
    Replies: 15
    Last Post: 17-08-2007, 02:01 AM
  3. Building a wine cabinet
    By Rory in forum Technical Discussions
    Replies: 38
    Last Post: 13-07-2004, 08:28 PM
  4. Mcquay water source heat pump
    By bernie in forum Air Conditioning
    Replies: 2
    Last Post: 10-02-2003, 01:53 AM
  5. Water Source Heat Pump
    By aliugur in forum Fundamentals
    Replies: 1
    Last Post: 02-06-2002, 03:24 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •