    Jan 2009
    NZ
    48
    35
    Question Mitsubishi Electric city multi
    Hi there,
    I`m currently installing a ciy multi system PQRY series with water heat exchanger in a big hotel complex.
    Has anybody got any experience with this system and if so, any common faults/problems while installing or during testrun?
    Sven
    Mar 2007
    Warwickshire UK
    723
    Re: Mitsubishi Electric city multi
    The water cooled PQRY system is exactly the same as any other ME City Multi system except for the water heat exchanger.
    So installation & commissioning procedures are all the same except for water flow rate.
    If you cannot directly measure the water flow rate then try this.
    Make sure you have plenty of heat load at indoor units
    Put complete system in test cool.
    When the compressor is ramped up to max speed
    measure temp diff water in / water out
    Aim for about 5 deg C diff with regulator valve & water flow will be near enough
    If the water circuit flow temp falls below 5 deg C or rises over 50 deg C the system will stop on water temp faults.
    Ideally you want flow temp arround 20 so at max cooling water out will be 25 & max heating water off at 15.
    If the water flow temp is higher then the system runs with higher than nessessarry discharge pressure & comp amps in cooling mode
    but if water flow temp is much lower than 20 then in heating mode then you start to get close to the low water heat exchanger fault conditions.
    So 20 is about safe water flow temp for max heat & max cool operations.
    Normal for main contractor to be late on finishing & commissioning water pipe installation.
    Mar 2006
    Lancashire
    1,859
    28
    A thanks would have been nice
    Marc
    Jun 2008
    India
    56
    64
    I agree with you Marc5180. Sumsor must be probably busy in installing his unit!!!
    People like me also got some good tips from Thermatech on water cooled VRF.
    Jan 2009
    NZ
    48
    35
    Hi there guys, I`m indeed very busy installing the system. 12 hr days 6 days a week and a one year old baby keeping me awake.
    First time since I`ve posted my question that i`m online again.
    But you`re right.
    Many thanks to Thermatech for the good advice. It`ll be another 10 month before the kommissioning starts, but I`ll try to give some feedback.
    Sven
    Jan 2009
    NZ
    48
    35
    Hi guys,I`m halfway through the job now(approx 40 CU`s and 200+ Fcu`s), and a problem I`ve struck is that I can`t get flow through some unit coils/BC unit.
    The Fcu`s are one PDFY P 32 VME and one PEFY P 250. The BC unit is a CMB p 104v GB slave box.
    I`ve struck the problem trying to purge nitrogen through the unit onnections for brazing. On the two FCU`s i couldn`t get any flow, tried with pressure up to 300psi, on the BC box i could only get flow through the low pressure liquid pipe, nothing through the other two main ports.
    Any suggestions?
    Sven
  1. Mitsubishi City multi problems
    By cooltech1 in forum Air Conditioning
    Last Post: 24-01-2010, 06:03 PM
  2. Mitsubishi City Multi PURY-P250 YMFC R407C
    By mick5 in forum Trouble Shooting
    Last Post: 10-06-2009, 07:50 PM